#176812 - 04/13/08 08:55 AM
Air curtains
|
Oh Well
Junior Member
Registered: 12/12/05
Posts: 3
|
Offline
|
|
Is it permissable to group two or more 3 phase air curtains on one feed? In addition to a blower they of course have a heating element. Also being as the only control is a three position rocker switch with an off position is a disconnecting device required? Thanks
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#176814 - 04/13/08 11:47 AM
Re: Air curtains
[Re: Oh Well]
|
leland
Member
Registered: 08/20/07
Posts: 396
Loc: Lowell area, Ma. USA
|
Offline
|
|
I would think "why not"? So long as your with in the ckt limitations. As for the disconnect: So long as it is within site of all three, and meets the load requirements. Why not?
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#176881 - 04/15/08 09:11 AM
Re: Air curtains
[Re: Oh Well]
|
Rick Kelly
Member
Registered: 01/11/06
Posts: 60
Loc: Iqaluit, NU, Canada
|
Offline
|
|
In a nut shell, yes and yes.
Rule 28-600(3) permits having more then one air curtain on a single disconnecting means.
Rule 28-602 describes what is permitted as far as a "disconnecting means" is concerned, and no, a three position selector switch is not adequate.
Rule 28-604(5) requires that the disconnecting means be located within 3m of the equipment and in clear sight. I would consider this equipment to be "air conditioning" equipment because of the heating element.
Rick...
|
|
Top
|
|
|
|
|
 |
 |
 |
 |