#176303 - 03/28/08 11:39 PM Bend Radius
Webmaster Administrator
Administrator


Registered: 10/07/00
Posts: 2568
Loc: NY, USA

Offline
 Quote:
How come Square D can violate the minimum bending radius rules and we can't?

Is there some exemption for manufacturers? I must admit, it's a pretty bend, probably done on some hydraulically operated jig at the factory.

Linda Evans


Top
Featured Tools
#176372 - 03/30/08 03:36 PM Re: Bend Radius [Re: Webmaster]
BigJohn
Member


Registered: 03/06/04
Posts: 341
Loc: Everett, MA

Offline
What is this equipment? No phase identification either?

Last time I saw bends even remotely close to those, the tool that had made them had also destroyed the insulation. I wouldn't be too happy to open a cabinet and find that.

-John

Top
#176374 - 03/30/08 06:08 PM Re: Bend Radius [Re: BigJohn]
InspectorE
Member


Registered: 10/08/04
Posts: 46
Loc: Hudson WI USA

Offline
Sorry about not giving more info. This is a Square D service entrance box (meter on left half) with 2 - 200 amp main circuit breakers in the right half. This is how it came from Square D. That's why I question why Square D can do this with a listed item. The insulation isn't broken on any of the 90 degree bends, I looked very carefully.
Top
#176389 - 03/30/08 11:35 PM Re: Bend Radius [Re: InspectorE]
Lostazhell
Member


Registered: 02/21/04
Posts: 1072
Loc: Bakersfield, CA (Originally Or...

Offline
It's not just Square D... I've seen the same in Cutler Hammer, Siemens, Allen Bradley, Furnas panels and MCC's out where I work..... UL governs safety of equipment, NEC governs safety of it's installation
Top
#176392 - 03/31/08 08:54 AM Re: Bend Radius [Re: Lostazhell]
ghost307
Member


Registered: 05/09/05
Posts: 304
Loc: Chicago Illinois USA

Offline
This looks like single conductor building wire with 600VAC insulation.

Which mimumum bending radius rules are they violating?
_________________________
Ghost307

Top
#176477 - 04/03/08 06:32 AM Re: Bend Radius [Re: ghost307]
SteveFehr
Member


Registered: 03/19/05
Posts: 923
Loc: Chesapeake, VA

Offline
They can do this because they test it like that, and it passes. They can do a lot of other things that are illegal per NEC, too, for the same reason- smaller conductors, for instance. NEC is rather conservative, as we all know.

So, don't look at it as exceeding the bend radius for cable, look at it as insulated cylindrical busbar!

Top
#176478 - 04/03/08 07:09 AM Re: Bend Radius [Re: SteveFehr]
IanR
Member


Registered: 12/06/04
Posts: 293
Loc: Palm Bay FL USA

Offline
Well put, Steve.
Remember the NEC has to be a very conservative catch all for many unseen installation parameters, that may or may not happen. The manufactures of these panels can test these units under controlled conditions. Then they specify the conditions, that these panels are used under, by listing them that way.

Top
#176482 - 04/03/08 09:20 AM Re: Bend Radius [Re: IanR]
InspectorE
Member


Registered: 10/08/04
Posts: 46
Loc: Hudson WI USA

Offline
"insulated cylindrical busbar"

I like that definition, maybe 2011 NEC will have it. Reminds me of the euphemism we used in the Army "aggressive retrograde maneuver" for run like hell.

Big difference between NEC and UL listing, ditto what the power company can do on their side of the meter.

Thanks folks!

Top
#176503 - 04/04/08 10:25 AM Re: Bend Radius [Re: InspectorE]
Zapped
Member


Registered: 10/01/02
Posts: 414
Loc: Huntington Beach, CA, USA

Offline
This is the norm for the internal wiring in meter/load-center pedestals. I have never encountered a problem resulting from this type of installation.
Top
#176723 - 04/10/08 12:00 AM Re: Bend Radius [Re: ghost307]
Nick
Member


Registered: 08/13/01
Posts: 603
Loc: Riverside, CA

Offline
 Originally Posted By: ghost307
This looks like single conductor building wire with 600VAC insulation.

Which mimumum bending radius rules are they violating?

I am with ghost. For under 600V what section is being violated??

Top
Page 1 of 1 1


Moderator:  electure, Trumpy, Scott35, Ryan_J, Roger, resqcapt19, renosteinke, pauluk, LK, iwire, dougwells, C-H 
Hop to:
Featured:

2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides
2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides


Tools for Electricians
Tools for Electricians

 * * * * * * * *

Electrical Chat
Join in a Live Electrical Chat!
Schedule:
 9pm EST
Wed - Business Chat
Friday - General Chat

>>
Login
 

  Sorry, your browser is not Java enabled, please visit our java support pages

in Chatroom

* * * * * * * *
Licensing Info and Lookup
Licensing Info
& Lookup

 


Generated in 0.104 seconds in which 0.013 seconds were spent on a total of 14 queries. Zlib compression disabled.

Live Chat

Join in a Live Electrical Chat!
Electrical Chat
Schedule:  9pm EST
Wed - Business Chat
Friday - General Chat

>> Login
 

  Sorry, your browser is not Java enabled, please visit our java support pages

in Chatroom

Recent Posts

Who's Online
4 registered (sabrown, electure, MattBrierley, JBD) and 18 anonymous users online.

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals