The Electrical Contractor Network Create and Share your own Electrical Related Photo Gallery! Electrical Safety Forum
Electrical Supplies Finder    Electrical Classifieds    Electrician Finder    ElectricalPhotos.com
Live Chat

Join in a Live Electrical Chat!
Electrical Chat
Schedule:  9pm EST
Wed - Business Chat
Friday - General Chat

>> Login
 

  Sorry, your browser is not Java enabled, please visit our java support pages

in Chatroom
October
Su M Tu W Th F Sa
1 2 3 4
5 6 7 8 9 10 11
12 13 14 15 16 17 18
19 20 21 22 23 24 25
26 27 28 29 30 31
Recent Posts
Top Posters
7667
pauluk
7375
Trumpy
4767
sparky
4343
iwire
4132
Bill Addiss
Who's Online
4 registered (sabrown, electure, MattBrierley, JBD) and 18 anonymous users online.
Page 1 of 2 12>
Topic Options
#175753 - 03/10/08 05:43 PM bond for pool
eddiecurrent
New Member


Registered: 03/09/08
Posts: 8
Loc: fl

Offline
i got a call to check pool lights for a costumer and noticed there was no #8 ground wire on any of the 2 pumps, lights, heaters, transformers,or sub panel.i didn't see any #8 solid at all in the sub panel.there was a stranded #8 or 10 from main panel.no ground rods at sub. they said the house was 6-8 years old.everything had lugs big enough for #8 including pumps.

my question is- does anyone know the codes for pool bond about 9-12 years ago?
i don't mess with pools much and am a new contractor.
i don't have code books past 2002.
since it's a ingrond concrete pool would the concrete act as a ground for the light, railing, and screen enclosure?
thanx for ur help.............

Top
Featured Tools
#175756 - 03/10/08 06:14 PM Re: bond for pool [Re: eddiecurrent]
KJay
Member


Registered: 11/27/07
Posts: 190
Loc: MA, USA

Offline
The #8 solid bonding requirement for pools has been in the code longer than I have been in the trade, and that’s since the early 1980's.
The #8 doesn’t need to go back to the panel, it only bonds the pool associated equipment together to create the equipotential bonding grid.

Top
#175758 - 03/10/08 06:20 PM Re: bond for pool [Re: KJay]
eddiecurrent
New Member


Registered: 03/09/08
Posts: 8
Loc: fl

Offline
same grid meaning light, transformer, pool pumps, railing,heater, screen enclosure,etc. right?
Top
#175759 - 03/10/08 07:04 PM Re: bond for pool [Re: eddiecurrent]
gfretwell
Member


Registered: 07/20/04
Posts: 4021
Loc: Estero,Fl,usa

Offline
You should also be picking up the rebar in the pool shell. If you don't see some #8 solid anywhere I am guessing this was not built with a permit. The bonding should have been inspected at least twice and maybe 3 times
_________________________
Greg Fretwell

Top
#175775 - 03/11/08 08:15 AM Re: bond for pool [Re: gfretwell]
BPHgravity
Member


Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida

Offline
We do three bonding inspections here in North Port. One at the shell, on at the deck, and one at the final.

I agree with Greg. If metal parts of the pool are not included in with the rest of the equipotential grid, such as shell steel, deck steel, metal handrails, niche light forming shell, metal within 5' of the water, ect..., a shock potential will be established between conductive parts.
_________________________
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

Top
#175778 - 03/11/08 09:50 AM Re: bond for pool [Re: BPHgravity]
Mike Wescoatt
Member


Registered: 06/17/01
Posts: 164
Loc: Cedar City, Utah

Offline
2002 NEC 680.26
The following needs to be bonded:
1. Metallic structural components
2. Underwater lighting (except listed LV w/ non-metallic forming shells)
3. Metal fittings (except for fittitng <4" in dimension that penetrate <1" into pool structure)
4. Electrical Equipment
5. Metal wiring methods and equipment within 5' horiz or 12' vertically

(c) ...with a solid copper conductor, insulated, covered, or bare, not smaller than 8AWG.

hth. Mike
_________________________
Mike Wescoatt

Top
#175788 - 03/11/08 03:55 PM Re: bond for pool [Re: BPHgravity]
eddiecurrent
New Member


Registered: 03/09/08
Posts: 8
Loc: fl

Offline
the same grid means all brought back to same ground bar or can the pumps be taken off pool panel and the rest be bonded to a ground rod???
Top
#175789 - 03/11/08 04:39 PM Re: bond for pool [Re: eddiecurrent]
leland
Member


Registered: 08/20/07
Posts: 397
Loc: Lowell area, Ma. USA

Offline
NOT GROUNDED. Just "bonded".

1 solid #8 from point to point to point unbroken. so essentialy they become 1 piece of metal, all of the same potential.

Top
#175803 - 03/11/08 08:28 PM Re: bond for pool [Re: leland]
BPHgravity
Member


Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida

Offline
The pool is already in contact with the Earth. Grounding of the pool and equipment will serve no purpose. The equipment grounding of the equipment will provide the effective fault path back to the source, while the equipotential bonding "shorts" out the battery created by the metal pool parts.
_________________________
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

Top
#176017 - 03/18/08 07:09 AM Re: bond for pool [Re: BPHgravity]
SteveFehr
Member


Registered: 03/19/05
Posts: 923
Loc: Chesapeake, VA

Offline
That, and although water and earth are conductors, they're relatively poor conductors and can still set up a situation where a swimmer becomes a current carrier, which is far more dangerous in a pool than anywhere else due to the reduced skin resistance, nature of the circuit (current is very likely to pass through the heart), difficulty of breaking contact, high potential to drown, and difficulty of rescue as anyone trying to conduct a rescue would be at the same risk.

The equipotential bond ensures there will be no equipotential difference within the pool and pool area, so that even if a short were to occur, the entire pool will be at the same potential and no dangerous amounts of current can flow through the water.

Top
Page 1 of 2 12>


Moderator:  resqcapt19, Roger, iwire, Ryan_J, Trumpy, Scott35, renosteinke, pauluk, LK, electure, dougwells, C-H 
Hop to:
Featured:

2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides
2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides


Tools for Electricians
Tools for Electricians

 * * * * * * * *

Electrical Chat
Join in a Live Electrical Chat!
Schedule:
 9pm EST
Wed - Business Chat
Friday - General Chat

>>
Login
 

  Sorry, your browser is not Java enabled, please visit our java support pages

in Chatroom

* * * * * * * *
Licensing Info and Lookup
Licensing Info
& Lookup

 


Generated in 0.106 seconds in which 0.012 seconds were spent on a total of 15 queries. Zlib compression disabled.

Live Chat

Join in a Live Electrical Chat!
Electrical Chat
Schedule:  9pm EST
Wed - Business Chat
Friday - General Chat

>> Login
 

  Sorry, your browser is not Java enabled, please visit our java support pages

in Chatroom

Recent Posts

Who's Online
4 registered (sabrown, electure, MattBrierley, JBD) and 18 anonymous users online.

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals