#175307 - 02/26/08 07:20 PM 70E Where stickers (Not 110.16) not 110.16 sticker
Yoopersup
Member


Registered: 03/04/03
Posts: 440
Loc: Michigan

Offline
NFPA says Hazard Analysis anything operationing at over 50 volts . That Means Mcc's, Switchgear, Panels 120/208
277/480 & up and up. I take it that includes Panels and Equipment over 50 volts Period. Example PLC 120 volt feed??
fire alarm Panel. 120/240 volt feed.
X ray Machine ect ect. Where is the Break Line and where in 70E does it say the break line is?? NEC 110.16 Spells out where ist sticker goes . 70E from what I see Doesn't where second one is required except Fer Hazard analysis. 2008 NEC adds Electrical Equipment to 110.16.look up equipment in definations in NEC umm this gets interesting??

Top
Featured Tools
#175310 - 02/26/08 08:39 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: Yoopersup]
JBD
Member


Registered: 07/12/01
Posts: 453
Loc: WI, USA

Offline
NFPA70E does not require any sticker/lables in addition to those in NEC 110.16.

70E requires appropiate PPE for all energized work above 50V. There is no relief.

There are several options available for determing the appropiate PPE, a full blown "arc flash" study based on IEEE 1584 is only one method.

Top
#175322 - 02/26/08 09:37 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: JBD]
Yoopersup
Member


Registered: 03/04/03
Posts: 440
Loc: Michigan

Offline
All over 50 volts covers a lotta ground.
Top
#175324 - 02/26/08 09:49 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: Yoopersup]
JBD
Member


Registered: 07/12/01
Posts: 453
Loc: WI, USA

Offline
 Originally Posted By: Yoopersup
All over 50 volts covers a lotta ground.


Yasure youbetcha.
Luckily, appropiate PPE is rarely a 40 cal "moon suit".

Top
#175326 - 02/26/08 10:04 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: JBD]
Yoopersup
Member


Registered: 03/04/03
Posts: 440
Loc: Michigan

Offline
But Like lets say you open a Fire alarm Pnl/ 120/240 >
voltage test ist with PPE on??? Sticker on Box??

Top
#175327 - 02/26/08 10:13 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: Yoopersup]
frenchelectrican
Member


Registered: 02/06/03
Posts: 577
Loc: forest junction .wi usa

Offline
 Originally Posted By: Yoopersup
But Like lets say you open a Fire alarm Pnl/ 120/240 >
voltage test ist with PPE on??? Sticker on Box??


That is good question because if my memory serve me right most FA panels are pretty much current limited type.

Merci, Marc
_________________________
Pas de problème,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#175329 - 02/26/08 10:41 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: frenchelectrican]
JBD
Member


Registered: 07/12/01
Posts: 453
Loc: WI, USA

Offline
There is no IEEE 1584 calculation for single phase circuits regardless of voltage so they are not normally part of arc flash studies therefore they rarely have a cal/cm² sticker on them.

If the calories or Hazard Risk Category (HRC) are not known you are only left with the 70E task tables. If the circuits are current limiting then you may be able to take advantage of the provisions that allow a reduction in the normal task table HRC.

How come the Wisconsin and UP guys are up at this time of night, don't you have to get up and shovel in the morning?

Top
#175330 - 02/26/08 10:53 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: JBD]
frenchelectrican
Member


Registered: 02/06/03
Posts: 577
Loc: forest junction .wi usa

Offline
JBD.,, This topic is almost parallel in other forum as well but not the excat same sisuation but i feel pretty simuair what you are talking about the Flash protection requirement need.


speaking of snow i only got dusting of snow [ about 30 CM or so { 1 1/2 inch } but right now it kinda windy now just got back from service call not too long ago the road start to get icy again ughh.

Merci, Marc
_________________________
Pas de problème,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#175343 - 02/27/08 06:38 AM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: frenchelectrican]
SteveFehr
Member


Registered: 03/19/05
Posts: 880
Loc: Chesapeake, VA

Offline
 Originally Posted By: JBD
 Originally Posted By: Yoopersup
All over 50 volts covers a lotta ground.


Yasure youbetcha.
Luckily, appropiate PPE is rarely a 40 cal "moon suit".
PPE for 51V is a cotton shirt and dry hands, isn't it?

Top
#175356 - 02/27/08 05:57 PM Re: 70E Where stickers (Not 110.16) not 110.16 sticker [Re: SteveFehr]
gfretwell
Member


Registered: 07/20/04
Posts: 3962
Loc: Estero,Fl,usa

Offline
How many amps Steve?
_________________________
Greg Fretwell

Top
Page 1 of 3 123>


Moderator:  Trumpy, renosteinke, Scott35, Ryan_J, Roger, resqcapt19, pauluk, LK, iwire, electure, dougwells, C-H 
Hop to:
Featured:

2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides
2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides


Tools for Electricians
Tools for Electricians

 * * * * * * * *

Electrical Chat
Join in a Live Electrical Chat!
Schedule:
 9pm EST
Wed - Business Chat
Friday - General Chat

>>
Login
 

  Sorry, your browser is not Java enabled, please visit our java support pages

in Chatroom

* * * * * * * *
Licensing Info and Lookup
Licensing Info
& Lookup

 


Generated in 0.107 seconds in which 0.015 seconds were spent on a total of 15 queries. Zlib compression disabled.

Live Chat

Join in a Live Electrical Chat!
Electrical Chat
Schedule:  9pm EST
Wed - Business Chat
Friday - General Chat

>> Login
 

  Sorry, your browser is not Java enabled, please visit our java support pages

in Chatroom

Recent Posts

Who's Online
3 registered (sparkyinak, renosteinke, cableguy619) and 22 anonymous users online.

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals