The Electrical Contractor Network Create and Share your own Electrical Related Photo Gallery! Electrical Safety Forum
Electrical Supplies Finder    Electrical Classifieds    Electrician Finder    ElectricalPhotos.com
Live Chat

Join in a Live Electrical Chat!
Electrical Chat
Schedule:  9pm EST
Wed - Business Chat
Friday - General Chat

>> Login
 

  Sorry, your browser is not Java enabled, please visit our java support pages

in Chatroom
September
Su M Tu W Th F Sa
1 2 3 4 5 6
7 8 9 10 11 12 13
14 15 16 17 18 19 20
21 22 23 24 25 26 27
28 29 30
Recent Posts
Top Posters
7649
pauluk
7333
Trumpy
4767
sparky
4343
iwire
4132
Bill Addiss
Who's Online
7 registered (gfretwell, drum, Scott35, staylor, electure, geoff in UK) and 26 anonymous users online.
Page 1 of 2 12>
Topic Options
#175136 - 02/23/08 09:16 AM Rooftop Equipment
highground
Member


Registered: 11/14/04
Posts: 49
Loc: Chama, NM

Offline
Hello,

I have a rooftop vent fan (3HP 480V) that the customer wants to control with a frequency drive. The panel is within sight (in the shop below). Is a disco required on the roof and prior to the drive to provide lockout capability, or does one on the roof suffice?

Also, do you guys provide additional motor protection in addition to the drive? (assuming it provides overcurrent protection)

Thanks in advance,

Top
Featured Tools
#175138 - 02/23/08 10:23 AM Re: Rooftop Equipment [Re: highground]
BPHgravity
Member


Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida

Offline
I don't exactly follow your installation description. However, Part IX of Article 430 identifies all your requirements for providing disconnecting means.

You will need to determine where and how you are obtaining both overload and ground-fault / short-circuit protection of the motor. It is possible this is all being doen by the VFD.
_________________________
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

Top
#175140 - 02/23/08 10:28 AM Re: Rooftop Equipment [Re: highground]
sparkyinak
Member


Registered: 07/08/07
Posts: 492
Loc: Alaska

Offline
You still need a disconnect on the roof if the motor i accessible on the roof and you can use a VFD down in the control room. You also want to check that the rooftop unit will not be affected by the VFD control like built in alarm or control circuits since the VFD is altering the power.
_________________________
"Good judgment comes from experience. Experience comes from bad judgment."

Top
#175145 - 02/23/08 11:22 AM Re: Rooftop Equipment [Re: sparkyinak]
Yoopersup
Member


Registered: 03/04/03
Posts: 444
Loc: Michigan

Offline
2005 N.E.C. 430.102 B States: Must be within sight of the MOTOR Unless meets Exceptions 430.102 (B) Exception (a)or(b).
Thats the way I read it anyway.

Top
#175157 - 02/23/08 12:44 PM Re: Rooftop Equipment [Re: Yoopersup]
sparkyinak
Member


Registered: 07/08/07
Posts: 492
Loc: Alaska

Offline
If the motor can be serviced from the roof, the disconnect downstairs will not be in site.
_________________________
"Good judgment comes from experience. Experience comes from bad judgment."

Top
#175159 - 02/23/08 02:23 PM Re: Rooftop Equipment [Re: sparkyinak]
Yoopersup
Member


Registered: 03/04/03
Posts: 444
Loc: Michigan

Offline
I agree that why I noted must be within sign . Kinda hard to see thru the roof!
BUT what if they had a skylight?
:))

Top
#177478 - 05/04/08 10:18 AM Re: Rooftop Equipment [Re: Yoopersup]
mikethebull
Junior Member


Registered: 03/18/07
Posts: 17
Loc: Rhode Island

Offline
I also agree although it is in 440.14. Also was a service receptacle within 25 feet or on the roof with the equipment this is 210.63.
Top
#177481 - 05/04/08 12:11 PM Re: Rooftop Equipment [Re: highground]
renosteinke Moderator
Moderator


Registered: 01/22/05
Posts: 3052
Loc: Reno Nv USA

content Online
From a practical standpoint, such a motor need two different types of protection; overcurrent as well as overload.
Overcurrent protection is what you get from fuses and breakers. Overload protection is what you get from the heaters in the starter. It's quite possible for a VFD to provide this secondary protection.

As for the disconnect ... I wish folks would forget the fine print of the code, and look at the application from a servicing standpoint. Do you want to shut it off before you work on it - or not? If so, doesn't it make sense to have some disconnecting means at the site of the motor? Why make / expect the guy to run up and down ladders multiple times, hope his LOTO is adequate, worry about automatic controls, etc?

Top
#177484 - 05/04/08 04:25 PM Re: Rooftop Equipment [Re: renosteinke]
NORCAL
Member


Registered: 09/25/02
Posts: 553

Offline
 Originally Posted By: renosteinke


As for the disconnect ... I wish folks would forget the fine print of the code, and look at the application from a servicing standpoint. Do you want to shut it off before you work on it - or not? If so, doesn't it make sense to have some disconnecting means at the site of the motor? Why make / expect the guy to run up and down ladders multiple times, hope his LOTO is adequate, worry about automatic controls, etc?


Thank you a little common sense is always in order.

Top
#177533 - 05/06/08 07:12 AM Re: Rooftop Equipment [Re: NORCAL]
resqcapt19 Moderator
Moderator


Registered: 11/10/00
Posts: 2161
Loc: IL

Offline
Mike,
 Quote:
I also agree although it is in 440.14.

Article 440 does not apply to vent fans.
_________________________
Don(resqcapt19)

Top
Page 1 of 2 12>


Moderator:  resqcapt19, Roger, iwire, Ryan_J, Trumpy, Scott35, renosteinke, pauluk, LK, electure, dougwells, C-H 
Hop to:
Featured:

2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides
2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides


Tools for Electricians
Tools for Electricians

 * * * * * * * *

Electrical Chat
Join in a Live Electrical Chat!
Schedule:
 9pm EST
Wed - Business Chat
Friday - General Chat

>>
Login
 

  Sorry, your browser is not Java enabled, please visit our java support pages

in Chatroom

* * * * * * * *
Licensing Info and Lookup
Licensing Info
& Lookup

 


Generated in 0.122 seconds in which 0.011 seconds were spent on a total of 15 queries. Zlib compression disabled.

Live Chat

Join in a Live Electrical Chat!
Electrical Chat
Schedule:  9pm EST
Wed - Business Chat
Friday - General Chat

>> Login
 

  Sorry, your browser is not Java enabled, please visit our java support pages

in Chatroom

Recent Posts

Who's Online
7 registered (gfretwell, drum, Scott35, staylor, electure, geoff in UK) and 26 anonymous users online.

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals