#175084 - 02/22/08 12:43 AM
cat 5 conduit fill
|
wacked
Junior Member
Registered: 12/19/06
Posts: 25
|
Offline
|
|
I don't have my code book handy at the moment but does anybody know the table to use for calculating cat 5 fill in a conduit? I came across this tonight while scoping out a job. ( 10 cat 5 in a one inch conduit )
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#175085 - 02/22/08 12:49 AM
Re: cat 5 conduit fill
[Re: wacked]
|
leland
Member
Registered: 08/20/07
Posts: 396
Loc: Lowell area, Ma. USA
|
Offline
|
|
How many pullers and how much lube do you have on hand?
Sorry. my silly side came out. But some truth to it.
I've no idea, not even sure if it's in the book.
Sorry again, Not much going on tonight for me.:)
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#175086 - 02/22/08 01:43 AM
Re: cat 5 conduit fill
[Re: leland]
|
homer
Member
Registered: 09/30/04
Posts: 28
Loc: Vancouver, WA, USA
|
Offline
|
|
Wacked, Data conduits often live by there own rules, but as I recall, 10 cables need about a 1-1/2 conduit, junction boxes every 100 feet and after every two 90 degree bends. Im fairly sure that there is somebody out there who is much smarter than I am who can quote the source. If you have to pull the cables, they pull hard unless they are a slick finish on the jacket. Try Google. Good luck, Larry
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#175095 - 02/22/08 11:12 AM
Re: cat 5 conduit fill
[Re: homer]
|
jay8
Member
Registered: 07/28/05
Posts: 101
Loc: Vancouver, BC
|
Offline
|
|
What you are probably refering to is TIA/EIA 568B Standards. Try putting this post on the voice/data section, and you will get your information.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#175097 - 02/22/08 11:51 AM
Re: cat 5 conduit fill
[Re: jay8]
|
ggardiner
Member
Registered: 10/22/01
Posts: 76
Loc: Calgary, Alberta Canada
|
Offline
|
|
According to a conduit capacity calculator from ADC/Krone 7 Typical 4-PR @ac .25" OD. in a one inch conduit. This would assume no more then 40% fill to allow for reasonable pull.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#175119 - 02/22/08 10:27 PM
Re: cat 5 conduit fill
[Re: ggardiner]
|
wacked
Junior Member
Registered: 12/19/06
Posts: 25
|
Offline
|
|
ggardiner, have you got an online link to this? Does the 40% rule apply???
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#175243 - 02/25/08 05:56 PM
Re: cat 5 conduit fill
[Re: wacked]
|
ggardiner
Member
Registered: 10/22/01
Posts: 76
Loc: Calgary, Alberta Canada
|
Offline
|
|
No what I have is a disc calculator that ADC gave me during a course on design I took from them two years ago.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |
 |
 |
 |
 |
#175300 - 02/26/08 12:58 PM
Re: cat 5 conduit fill
[Re: ggardiner]
|
mikesh
Member
Registered: 06/07/06
Posts: 187
Loc: Victoria, BC, Canada
|
Offline
|
|
I answered this in the other place you asked. 12-1014 Give the rules for wire fill in raceways and the type of load has no bearing. %40 for more than 2 cables up to 200 cables max.
|
|
Top
|
|
|
|
|
 |
 |
 |
 |