#175075 - 02/21/08 08:21 PM Odd panel label, etc....
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1075
Loc: Bakersfield, CA (Originally Or...
This panel feeds most of the general loads at the Co-gen for the company we work for... I've not seen 240Y/120V anything before... then it says 1Ø and there are 3Ø breakers inside (I haven't had a chance to remove the cover, I'm almost afraid to!) nor do I know the meaning of "bypass", but I'm hoping it isn't a backfeed from the UPS system.

The last pic is in the room with the UPS batteries and inverter... No one I've talked to can offer a clue as to why the fan was installed this way!















Top
Featured Tools
#175078 - 02/21/08 09:29 PM Re: Odd panel label, etc.... [Re: Lostazhell]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 503
Loc: Alaska
Few guesses would be:

1. The 3 poles are terminated only on two legs. The cheap thing to when you have a couple of spares sittng around and plenty of spare spaces to waste.

2. The wrong dead front was put on from a single phase panel

3. Split bus-panel

Longshot on them all but I go with number 1. I like the "service diconnect" for the fan? at the bottom of the post.
_________________________
"Good judgment comes from experience. Experience comes from bad judgment."
Top
#175083 - 02/21/08 10:39 PM Re: Odd panel label, etc.... [Re: sparkyinak]
leland Offline
Member
Registered: 08/20/07
Posts: 411
Loc: Lowell area, Ma. USA
___No one I've talked to can offer a clue as to why the fan was installed this way!____

I work "inside". I know why.
They are too damn lazy to go to the supply room and get what they need!!! It may run into their break!!!.
All day to do it right! No time limits, etc,etc,etc... Yet, this is what they do.
Disgusting.

I see it every day. No way do I meen to infer that all inside guys/gals are this way. BUT.. the majority are!

Thats sad.
Top
#175091 - 02/22/08 03:04 AM Re: Odd panel label, etc.... [Re: leland]
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 590
Loc: forest junction .wi usa
FDB breaker in that Box ?? it sure don't look right at all and very instering to see the label printed wrong if that is the case.

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top
#175103 - 02/22/08 02:53 PM Re: Odd panel label, etc.... [Re: frenchelectrican]
techie Offline
Member
Registered: 05/17/05
Posts: 213
Loc: palo alto, ca usa
I suspect that the fan is wired that way so that the fan can be plugged in to the UPS during an extended outage.

Is there a transfer switch at the UPS output, or maybe built in to the UPS to allow the load to be powered while the UPS is taken offline for servicing?

Is there a transfer switch to allow the UPS to be powered by a generator, separated from the building power? That could also explain the fan wiring, since during heavy charging is when you would really want to have that fan operational.
Top


Featured:

2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides
2008 NEC & Related Books, Tabs, CD-ROMs & Exam Prep Study Guides


Tools for Electricians
Tools for Electricians

 * * * * * * * * Licensing Info and Lookup
Licensing Info
& Lookup

 

Recent Posts
Facial hair?
by Electricmanscott
Today at 05:32 AM
Your Call Taker, The Business Bottleneck
by Electricmanscott
Today at 05:27 AM
How do I make UK appliances run in the US
by Trumpy
Today at 03:09 AM
Tamper resistant: 406.11
by gfretwell
Yesterday at 07:49 PM
Surge outlet
by pdh
Yesterday at 06:44 PM
Top Posters (30 Days)
gfretwell 84
renosteinke 43
Trumpy 35
Webmaster 30
HotLine1 25
November
Su M Tu W Th F Sa
1
2 3 4 5 6 7 8
9 10 11 12 13 14 15
16 17 18 19 20 21 22
23 24 25 26 27 28 29
30

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals