Posted By: ianh Bulbs Blowing Frequently - 09/16/05 01:19 PM
Hi Guys

One of the most common complaints I get from our customers is that they go through a lot of bulbs in their properties.

When I get these complaints, I install voltage recorders and if the supply voltage exceeds oour limits (216 to 253V) then I can alter the local transformer to bring it into line.

If the customer lives close to a distribution transformer, they can experience a high average voltage (240V+) but not exceed the threshold.

As all bulbs are manufactured for European 230V systems they tend to get a bit upset when subjected to 240V+ for long periods of time.

Has anyone got any thoughts on how people could get around this problem? One customer told me that he had sourced light bulbs manufactured for 250V systems and they lasted a long time, but I can't find any suppliers who would be able to supply them.

Any thoughts or cost-effective solutions would be appreciated.

thanks

Ian
Posted By: chipmunk Re: Bulbs Blowing Frequently - 09/16/05 06:26 PM
My first thought was a bucking transformer, one with a 12v output would work for to drop 240v to 228, thus bringing it into line with 230v bulbs.

Normal low voltage lighting transformers may or may not have the required primary to secondary voltage withstand and insulation resistance figures, but it would be worth looking at.

A simpler solution (more DIY than professional however) would be a dimmer switch inline with the normal switch, somewhere inaccessible, set to drop the voltage to 230v rms or even 220, thus increasing the life of the lamps.

Other possible solutions that crossed my tiny mind were back to back zener diodes, and resistors, both of which would require protection, and plenty of heatsinking, even with a 40w bulb as the load. (dropping say 20v at the current required by a 40w lamp still comes close to 4 watts, which in an enclosed area requires plenty of heatsinking).

Other 'sideways' solutions would involve CFL or LED lamps thus bypassing the problem of filament lamps altogether, and increasing lamp life and reducing the power bills as an addition.

I expect this problem to become more common now equipment is being produced for 230v, although our brethren on the European mainland are probably experiencing longer lamp life due to the same causes.

I suspect that the 'super long life rugged' lightbulbs available a few years ago were in fact merely designed for 250-260v, thus providing enormous life on 230-240v supplies, I suspect the 60w version was in fact a 75watt 250v lamp being underrun. I haven't seen these for a few years now but they may also be a solution.
Posted By: Trumpy Re: Bulbs Blowing Frequently - 09/17/05 07:08 AM
Ian,
If it has become that much of a problem,
fit a DIN Rail mount Surge Diverter to the incoming Mains.
These clamp voltages in excess of 253VAC.
What you should be looking to get rid of is voltage spikes.
Incandescent lamps do not like shocks to the filament and will blow a lamp as quick as.
Before you address the lamp issue, address the voltage spike issue.
That is not to say that lamps made these days are nothing short of rubbish. [Linked Image]
Posted By: classicsat Re: Bulbs Blowing Frequently - 09/17/05 01:33 PM
Try to find industral/agricultural bulbs. Around here, they sell farm rated bulbs, which are rated 130V.
Posted By: pauluk Re: Bulbs Blowing Frequently - 09/17/05 03:00 PM
Quote
My first thought was a bucking transformer,

That doesn't sound like a bad idea actually, and easy to implement with our separate lighting circuits rated at no more than 5 or 6A rach.

It wouldn't help lamps plugged into general-purpose outlets, but it would cover most of the lights.
Posted By: renosteinke Re: Bulbs Blowing Frequently - 09/17/05 04:42 PM
I've been hearing many reports on thes side of the pond about bulbs quickly burning out.

Many times, this seems to be because the "cheap" bulbs- especially the ones that come with the appliances- are not rated for the actual voltage applied. (Our new areas often have 127v (measured) vs. the 110v (rated) bulbs supplied. The problem is usually solved by using 130v rated bulbs. But....

There are enough remaining complaints that I wonder if something else is happening. Sure, we have several types of "rough service" bulbs, and those address problems caused by vibration and thermal/ mechanical shock.

Still, I would not be the least bit surprised if the manufacture of bulbs has advanced to where the glass is thinner, the filaments finer, than they once were. My lighting suppliers assert that the big discount stores get 'factory seconds' bulbs. And many of our bulbs are made in China- which has a rather abstract concept of "quality control." (Summed up in the phrae 'close enough-doesn't matter (silly gweilo)')

Dodging the issue, I have developed a preference for compact fluorescent bulbs. Ordinary lights just seem so....yellow. These bulbs seem to come in two varieties- the ones that quickly fail, and the ones that run forever. There's that QC issue again. The ballasts in them ought to eliminate any surge or harmonic related problems, though.

Which may be why the ordinary bulbs are failing. These days, we have all sorts of household electronics, everything from the TV to the microwave. These may be 'dirtying' up our supply, and contributing to bulb failure. I just don't know.
Posted By: gideonr Re: Bulbs Blowing Frequently - 09/17/05 05:11 PM
Could it be anything to do with the inrush currents? Filament bulbs have a very low resistance cold, I measured 65 ohms for a 60W 240v bulb, which would be 960 ohms at full brightness. Lower impedance supply wiring would reduce the life of the bulb.
Posted By: Alan Belson Re: Bulbs Blowing Frequently - 09/17/05 05:16 PM
"Ah so! Old Chinese proverbs, Grasshopper:

"Han make lights, many work."

"Voltage? Fluctuations!"

"And, Ahso to you as well!"
[Linked Image]
Alan
Posted By: aussie240 Re: Bulbs Blowing Frequently - 09/18/05 12:21 AM
260V bulbs used to be easy to get here...they were made for use in Western Australia which until the 1980's ran on 250V (in reality up to 265V in some areas) Here on the east coast using those bulbs on 240V would give an exceptionally long life...so long in fact that the glass would have become blackened by filament evaporation before it actually burnt out. I'd get several years out of a bulb that was used every day. I was surprised to find 260V bulbs again after about 15 years in the local Bunnings. I do know that Crompton still make 250V bulbs. I've gone off CFL's for my own use...they can't handle mains spikes and the RFI is annoying. The first generation of Philips CFL's with iron cored chokes were great though. It's been about 10 years since the "240-250V" rating was printed on our light bulbs (were they really 245V I wonder?). Now they're all simply "240V".

In my garage is a 300W GES based light bulb. To prolong its life I have a 40 ohm resistor in series with it to absorb the initial inrush current. After a few seconds the resistor is shorted out by means of a time delay relay (ie. a 555 timer IC driving a 12V relay). It seems to work very effectively as the bulb comes up from a gentle glow as the filament heats up and the current drops before the full voltage is applied.

The idea of using a transformer to reduce voltage is a good one; you can use a halogen light transformer with the 12v secondary connected out of phase in series with the load. I had to do a similar thing with my fridge which would trip the thermal cutout in hot weather... yet another appliance fitted with a 220V 60 cycle induction motor foisted on the Australian public.

[This message has been edited by aussie240 (edited 09-17-2005).]
Posted By: C-H Re: Bulbs Blowing Frequently - 09/18/05 03:01 PM
This is a well known problem in Scandinavia too. There used to be two sorts of bulbs: 220-230V and 230-240V. Now they have 230V bulbs. However, as a special item, there are 240V bulbs for buildings with "elevated mains voltage", i.e. close to the transformer. Aren't such available in the UK?

Osrams catalogue lists both 230V and 240V bulbs:
http://www.osram.se/Bilder/PDF/Allm%c3%a4nbelysning/Glodlampor.pdf
Posted By: aussie240 Re: Bulbs Blowing Frequently - 09/19/05 04:29 AM
Did Europe actually increase the voltage to 230, or is it like the Australian and UK 230V and "on paper" only?
Incandescent bulbs are much more voltage critical than say heating elements or motors and one would presume the voltage stamped on the bulb is what voltage it is meant to run at [ie. a 230V bulb means that...not 220 or 240 in disguise].
My guess is that's why Aussie bulbs (and I have seen somewhere also UK ones...can anyone confirm?) are still stamped with 240V because that's what the supply voltage really is despite what might be written in the pages of bureacracy. Real 230V bulbs sold here would have a slightly shorter life and would probably result in complaints to various consumer protection agencies.
Posted By: djk Re: Bulbs Blowing Frequently - 09/19/05 08:17 AM
Until relatively recently in Ireland our bulbs were mostly rated 220V. The voltage is now nominally 230V and tends to be somewhere between 215 and 235V in most instances.

I wonder if it's possible that the bulb manufacturer is just making 220V bulbs and sticking 230V labels on them?

It's quite possible that they havent' changed their specs at all.

240V bulbs used in Ireland tended to last for ridiculously long times. There were stories of people crossing the border to northern ireland to pick up bulbs as they lasted far longer.

[This message has been edited by djk (edited 09-19-2005).]
Posted By: Texas_Ranger Re: Bulbs Blowing Frequently - 09/19/05 07:44 PM
Depends on where you are. At home in Vienna and in our home in a small (population 460) next to the Czech border I always get close to 235V. At school in Vienna (roughly 5km from home, but has it's own 10kV to 220/380V) I never got more than 225 to ground and 382 between phases.
Different brands of bulbs had a widely varying life expectancy here. For some time we had cheap, IIRC Patria bulbs that would blow frequently, now we have Philips that last almost forever.
Posted By: Trumpy Re: Bulbs Blowing Frequently - 09/25/05 08:37 AM
Hang on a second,
Lets look at the design of a modern light bulb.
10 years ago, the filaments were thicker and used double coil technology.
We can't compete here in NZ or for the matter any Non-asian country, in manufacturing the bulbs here.
Our last bulb factory closed in 1999.
Add to that the fact that bulbs had a fuse in them too, now they don't.
What annoys me most of all is the fact that these bulbs are advertised as "Long-life" bulbs, knowing full well that the customer will be purchasing a new bulb at the next voltage surge.
I've been to houses where they burned out 10 lamps with a flick of a switch.
Posted By: marcspages Re: Bulbs Blowing Frequently - 09/25/05 08:51 AM
Hi guys,

I wrote on both of these ages ago already - after being flooded with reports of "short lamnp life". We're about to move our clocks again and, strangely, this is when the emails will start up again as this is when lamps are run for longer each day.

see here and
here

M.
Posted By: pauluk Re: Bulbs Blowing Frequently - 09/25/05 10:46 AM
Excellent point on the handling of bulbs there Marc.

How many times has anyone seen the shelf-stackers in the supermarket drop a box?

"Oops! Oh well, doesn't appear to be broken, shove them on the shelf."
Posted By: RODALCO Re: Bulbs Blowing Frequently - 12/09/05 10:13 AM
We used to be able to get the "Performer" brand lamps via K mart in New Zealand, rated at 240 - 250 Volts. I have checked their life with hour meters and they seem to last for around 2300 hrs before failing.
At promotions they were sold for around NZ$1 ea. The voltage in West Auckland is usually around the 230 - 236 Volts range.
Normal 230-240 V lamps in the house I have checked usually last for about 800 hrs. A date written on the base of the lamp is also a very good idea, because we forget sometimes when things were replaced last time.
Posted By: pauluk Re: Bulbs Blowing Frequently - 12/09/05 11:03 AM
[Linked Image]


Quote
A date written on the base of the lamp is also a very good idea, because we forget sometimes when things were replaced last time.

A habit I picked up from my late father is to put a small sticker with the date of replacement on batteries too. It's especially handy on things where the battereies are replaced only very infrequently, such as quartz clocks, test meters, etc.
Posted By: Trumpy Re: Bulbs Blowing Frequently - 12/09/05 04:40 PM
Personally I buy my bulbs from Ideal Electrical.
I gave up on supermarket lamps years ago, the quality between two bulbs doesn't seem to be consistent.
Sure, you might pay a wee bit more per bulb, but as they say, you get what you pay for.
BTW I was at the supermarket getting the groceries the other day, bulbs were $0.45 each, if I remember correctly, they had a brand name I've never heard of before. [Linked Image]
Posted By: Texas_Ranger Re: Bulbs Blowing Frequently - 12/09/05 07:56 PM
Today we worked on a big fan unit, doing all kinds of physical metering. At school Voltage is usually low, like 378V between phases. But today we got 355... I suspect a faulty meterm but still it was hefty.
Posted By: aussie240 Re: Bulbs Blowing Frequently - 12/11/05 10:52 PM
Quote
We used to be able to get the "Performer" brand lamps via K mart in New Zealand, rated at 240 - 250 Volts

Undoubtedly the same bulbs sold stacked on the shelves in the Australian K marts. Aussie light bulbs have been rated at 240-250V for many years to take into account 250V being present in many areas.
I suspect Kmart (and most Kiwis & Aussies) aren't aware of the 10 volts nominal difference between the two countries...after all NZ is seen as the de facto 7th state here and with the electrical fittings being the same no one thinks twice.
Posted By: ianh Re: Bulbs Blowing Frequently - 01/04/06 05:01 PM
Hello

Thank you very much for all your input on this issue. You have given me lots of food for thought and helped me to put a leaflet together that I can give to people to allow them to see the other things that could cause their problems.

Cheers

Ian