Posted By: kiwi C.T. chamber covers - 05/07/05 08:35 AM
In a couple of instances here in NZ I have had Inspectors who require extra plastic shrouding over metering CT busbars, even when the busbars are in a completely sealed chamber with metal fixed covers which require two tools to remove, engraved warning labels and are sealed with the power authority seal which only authorised persons are allowed to break. Add to this the fact that the Main Switchboard should be in a locked room and this requirement for additional plastic shrouding just seems frivolous.

The 1% of inspectors who raise this requirement always cite Reg 94, which states "all practicable steps must be taken to prevent accidental contact with live parts through the use of barriers and screens etc". It seems that the whole matter hinges on the interpretation of the word "practicable".

In all cases the Inspector will require that an extra plastic cover-plate be fitted under the metal fixed cover. This plastic cover-plate will take 15 seconds to remove for anyone with the same tools used to remove the metal fixed cover.

The only reason anyone needs to access a CT chamber is for CT maintenance when the meter stops running and in this case the main switch has to be switched off.

I am not ragging individual inspectors here, and in no way do I think my opinion is final. I would like to hear other members thoughts on this matter, especially from Australasia and the UK.
Posted By: gideonr Re: C.T. chamber covers - 05/07/05 11:44 AM
I don't think either the inspectors or installers are at fault here, it's that the code is too vague. It should simply state that all parts needed for type approval must be fitted. Given the number of photographs on this forum of installations left without their covers on, and of other cables routed through cabinets, double insulating busbars has its merits.
Posted By: Trumpy Re: C.T. chamber covers - 05/07/05 08:39 PM
kiwi,
That's a rather good point.
I've heard of this sort of thing being asked for before, not locally, but there was an Inspector making all sorts of noise about it at a recent Refresher course I attended.
CT busbar chambers by thier nature, as you have mentioned are sealed equipment and would normally be only accessed by Authorised personnel, the ones we use down here use a security screw system.
For those outside of NZ:
Quote

Reg. 94. Protection against direct and indirect electrical contact-
(1)A person having control of any works, electrical installation, electrical appliance or associated equipment must take all practicable steps to minimise the risk of direct or indirect contact with the works, electrical installation, appliance or associated equipment.
(2)Compliance with any of the following criteria is deemed to be compliance with subclause (1):
(a)Prevention of the passing of an electric current through the body of a person or limiting that current so that shock currents and thier duration cannot exceed the IEC shock currents standard:
(b)Automatic disconnection of the power supply to the works, electrical installation, appliance, or associated equipment, as the case may be, on the occurence of a fault:
(c)Use of screens, barriers, or fittings which prevent direct or indirect accidental contact with the live fittings or exposed conductive parts.


Oddly enough, we are told at work that all CT equipment is to be shut down before accessing the transformers, it's in our Health and Safety policy.



[This message has been edited by Trumpy (edited 05-07-2005).]
Posted By: Trumpy Re: C.T. chamber covers - 05/08/05 01:42 AM
Kiwi,
One thought just struck me.
As I understand things, (I could be wrong here too) the 1997 Electricity Regulations are no longer in force.
Instead guidance should be sought from AS/NZS 3000:2000, as far as I'm aware these superseded the old Regs.
Section 1.7: Protection for Safety applies to this sort of thing.
In particular, sub-sections 1.7.1- 1.7.4.3.
Hope this helps.
Posted By: kiwi Re: C.T. chamber covers - 05/08/05 04:22 AM
I was under the exact same impression as you Trumpy. I thought the Regs had been superceded. Apparently not ! Someone from the Energy Safety Service told me last week that the old Regs HAD NOT been superceded but INTEGRATED.

We are now in a situation where we must reference the Regs, the AS3000, the companion standards to AS3000 and some of the old codes of practise, the Act, and any Bulletins the ESS publishes on specific issues. Joe Sparky is going to have to tow a mobile library behind his van to keep up.

Once again there are government officials drawing enormous salaries here and producing zero results. They won't accept responsibility for, and are too lazy to produce a single standardized document with clear rules and guidelines, a document where the buck stops and where the government takes responsibility for its regulations it forces us to uphold.

This situation is another example of government bludgers getting between Joe Sparky and his hard earned dollars and not really helping him.
Posted By: kiwi Re: C.T. chamber covers - 05/08/05 04:33 AM
Sorry Guys I was off on a rant there. Thanks for your input Gideonr and Trumpy. It does seem like a good idea to double insulate CT bars. I guess what I was looking for was a constructional requirement or specification which would put this matter to rest, and not be left up to Inspectors and Installers to argue about at crucial commissioning times.
Posted By: Trumpy Re: C.T. chamber covers - 05/08/05 12:05 PM
kiwi,
Before we start getting too ridiculous here,
I've shot an e-mail away to a friend of mine that I did my time with as an Electrician.
He's now 2IC to the Chief Electrical Engineer (or there is bound to be a new title for everyone, with it being a Government Dept).
(Didn't I just draw the short straw!!) [Linked Image]
But I will post the results of that e-mail here.
Now kiwi, one thing you must make clear, is this requirement from a design point of view, or from an installation point of view?.
I've unloaded some big switchboard units before and the person has asked me to inspect them and make sure that they comply before they are signed off as delivered.
Luckily they have complied (for my skins sake).
Just let me say this though, all local switch-board manufacturers do know the
Regulations and Codes of Practice here, to sell non-compliant gear here in a small market like NZ, will shut you down in no time flat.
I also believe that you have to be a Registered Electrician to even assemble Switch-boards here.
Could kiwi, confirm that?.

[This message has been edited by Trumpy (edited 05-08-2005).]
Posted By: pauluk Re: C.T. chamber covers - 05/08/05 10:35 PM
Just my opinion, as I'm not generally involved with this sort of equipment, but I would have thought that the single cover does indeed constitute a "practicable" solution which is quite adequate in preventing contact with energized busbars.

Maybe extra insulation would be of added benefit if work needed to be done inside the chamber with power on, but that's not quite the same thing.
Posted By: marcspages Re: C.T. chamber covers - 05/09/05 09:13 AM
Hi guys,

Could I throw in a ha'penny worth here, done from a rather practical problem I keep facing when having to do (pukka) power quality investigations.

My beef is you either have nowhere to clamp on the CTs and/or voltage croc clips, or you have wide open busbar.

I would so love to see a set of (preferably double) insulated busbars where the CTs can go, and then studs for the voltage take-off (maybe the voltage can have an 'inverted-L' shape cover to stop direct contact). It appears the switchpanel designers don't see 'testing' ever being needed.

M.
Posted By: kiwi Re: C.T. chamber covers - 05/09/05 10:37 AM
Thanks again for the help guys. Trumpy, I think this is a design issue because switchboards must be designed to comply with Regs, Codes, Standards and OSH requirements. AS 3439 definitely implies that the extra plastic shrouding is unnecessary if a tool is needed to open the CT cabinet and "Authorised Persons Only" seals and labels are used. And if creepage and clearance distances are compliant.

Paul says the extra shrouding is a good idea and I agree. There are Meter Potential fuses on the CT busbars and I guess you should be able to change those fuses with a plastic shroud still over the CT bars.

According to the Act Trumpy, switchboard builders who do the prescribed wiring and the testing have to be licensed. Bolting cabinets together etc can be done by anyone.

Its uneconomical but our guys insist on building their own boards, metalwork and all. They're too fussy to let a labourer do their metalwork. In Australia its common for electrical mechanics and labourers to assemble cabinets and even do busbar work.
Posted By: kiwi Re: C.T. chamber covers - 05/10/05 10:09 AM
Hi Marcspages. Insulated bars & testing tap-offs with removable covers are a great idea but unfortunately would triple the cost of a CT chamber, and Electrical Engineering Consultants always have one eye on the money and don't consider making safe provisions for power analysis testing without a shut-down later on.

I guess the Metering CT chamber is an obvious choice for live power analysis meaurement when a shut-down is inconvenient

I can imagine how putting clamps & croc clips on bare bars could be very nerve-racking. I would wear a welding helmet and a thick pair of rubber gloves.

The OSH rules in NZ forbid persons working on or in the vicinity of live parts. Unless there is an approved procedure in place to minimise risk of injury etc.

So unless their is a CT chamber with properly shielded testing points, the main switch should be off while you connect your test leads. This may mean that you have to get up in the middle of the night to do the shut-down, but its still preferable to attaching leads to bare live bars. Fault currents are very high at CT busbars and one tiny mistake can cause a big bang.
Also you can charge more for "after-hours work".
Posted By: marcspages Re: C.T. chamber covers - 05/10/05 04:16 PM
Kiwi,

"Sir, I need to throw the big switch on your bank's data centre while I connect my PQ recorder". Yeah, right!

In actual fact, I have only had one client (oh yes, it was a bank too!) to date who would not let me connect live - to their detriment! Before I could connect up the kit at the next scheduled shutdown, they lost their data centre because of a set of loosening busbar bolts (something the PQ survey would have picked up).

Strangely, I don't get the shivers with open busbars. It's more for the cowboys I've seen in action. I'm more than happy to work live to 690VAC (or thereabouts - I get vertigo at 1kV).

But I ramble, the whole purpose was merely a ha'penny thought should it influence someone to put in reasonably costed testing facilities for our modern power-hungry world!

Marc.
Posted By: chipmunk Re: C.T. chamber covers - 05/10/05 04:37 PM
It's a sad fact that people who are not electrically qualified can say 'no you can't shut that down' [Linked Image]

My answer would probably be seen as confrontational, but it does make a point. That would be "It can't be shut down? Oh good, that means you have it on a UPS right?" *CLUNK*... [Linked Image]
Posted By: pauluk Re: C.T. chamber covers - 05/11/05 11:35 AM
Quote
That would be "It can't be shut down? Oh good, that means you have it on a UPS right?" *CLUNK*... [Linked Image]

Good one! [Linked Image] It does make you wonder how many of these "can't be interrupted" supplies do have a UPS backup though, doesn't it?



[This message has been edited by pauluk (edited 05-11-2005).]
Posted By: chipmunk Re: C.T. chamber covers - 05/11/05 08:36 PM
There are occasions where this wouldn't apply.
Namely: In a hospital or place where there was other medical equipment, in any place where the other guy's bigger than me, and if the breaker/switch was on the output side of a large UPS, that just ends up making you look like a doofus [Linked Image]
Posted By: Trumpy Re: C.T. chamber covers - 05/12/05 08:32 AM
That's a rather good point Paul.
For those people that have installations that "Can't be shut off", it is up to them to have a back-up power supply system.
I've heard just about all of the various excuses as to why the power must stay on and I haven't heard any that are convincing enough yet.
kiwi,
Just a little note about "Inspectors".
I was talking to a Power Company Inspector at work the other day and he said that the term "Electrical Inspector" doesn't have the same meaning as what it did before 1992.
He said that to even get an Inspectors Licence, is so simple it's not funny these days, considering that you only have to have 3 years qualifying experience and sit an exam to get there.
When he did his, you had to have 15 years qualifying experience as a Registered Electrician, hold Advanced Trade Certificate
and sit a 4 hour written exam.
He also said that a lot of the newer Inspectors these days gave inconsistant rulings on various work, often picking up little things, but leaving out serious safety issues.
Posted By: kiwi Re: C.T. chamber covers - 05/17/05 09:51 AM
Excellent point Chipmunk ! Often, an unplanned shutdown is the best way of testing the health of auxillary and emergency electrical services in a large building. Managers who get twitchy over unplanned shutdowns always change their opinion when they find that the emergency lights in the stairwell did'nt start or that the airconditioning did'nt restart.

I believe that working on live equipment is to be avoided or at least undertaken in controlled situations where the risks are minimised to ridiculously low levels. We have all been obliged to work in live situations at one time or another to make the corporate budget, and we have all seen the results of the accidents.

I think the safe testing tap-offs for main switches that Marcspages longs for are the answer. Now someone just needs to convince the bean-counters and they can start specifying this in their designs.


Trumpy I had no idea that it was three years experience required for Inspectors. Jeez that means that you could spend three years drilling holes as an apprentice then another three after your registration wiring cottages then the next day your an Inspector certifying a 2400A central supply for a shopping mall. An extreme example I know, but I think it highlights the pitfalls of NZs electricity deregulation.
Posted By: Trumpy Re: C.T. chamber covers - 05/24/05 10:28 PM
Finally an answer, from Bill:

Quote
The Regulations are still the main driver for safety, have not been replaced
by standards and are law. A number of the ECPs were replaced by AS/NZS 3000
and companion standards. Reg 69A calls up and mandates those relevant bits
of AS/NZS 3000.

In reference to your technical enquiry you are correct, an enclosure that
requires the use of a tool to access live parts would be deemed to be
electrically safe and meet reg 94(c) and also AS/NZS 3000 cl.1.7.3.4.2.

I can see no requirement in the regs or standard for the additional plastic
shield. In fact if this was not made of the appropriate fire resistant
material it may introduce another hazard. The CT chamber may be an
engineered design to the relevant switchboard standard and passed those
tests in accordance with that standard.

I would assume that this is a commercial or industrial installation and
there is virtually no risk of unauthorised persons unscrewing covers on
switchboards.
Hope that this helps. [Linked Image]
Posted By: kiwi Re: C.T. chamber covers - 06/08/05 09:29 AM
Thanks for that reply Trumpy. It confirms that the way CT chambers are constructed in the industry right now is compliant. No drastic (expensive) changes are required.

I see the EWRB has issued an email today announcing that they have struck a deal with Standards New Zealand to make standards documents, referenced in the Regs, available online.

Guess I'll have to take back my comments on "government officials not helping Joe Sparky" now!

Shucks !
Posted By: Trumpy Re: C.T. chamber covers - 06/09/05 02:53 AM
Thanks for the info kiwi! [Linked Image]
Quote
I see the EWRB has issued an email today announcing that they have struck a deal with Standards New Zealand to make standards documents, referenced in the Regs, available online
So does that mean that we won't have to fork out huge amounts of our hard-earned money to get the standards we need?.
Did the e-mail state which standards would be offered?.

Cheers mate. [Linked Image]
Posted By: kiwi Re: C.T. chamber covers - 06/09/05 10:58 AM
The full list of the available standards is on the EWRB website Trumpy. Sorry I don't know how to post links.

As unbelievable as it sounds. Yes the EWRB is giving us something for free. Those standard documents aren't cheap.