Belgian,
Thanks for sending the plans. We'll now inundate you with about a hundred questions!
I see that you have a washing machine and dryer in the bathroom (I don't know any Flemish, so I'm guessing that's what
Wasmach and
Droogkast are on circuits K and L). Is this a common location? I've seen such an arrangement elsewhere in Europe, but it's quite rare in the U.K.
All your branch breakers (except cct. N) are marked as 2-pole. Is it normal to open the neutral on branch ciruits there now? I heard that this is now the norm in France.
The bathroom water heater appears to be the only 3-phase load, and from the 4 x 2.5mm designation on the cable and the 3-pole MCB, I take it that this has delta-connected 380V elements. Correct?
It seems that your PoCo really wants a lot of details before they'll connect. One other point I noticed though: The diagram gives full details of which outlets are on which branch circuits, but there's no indication of which phase serves each circuit. Are they not too bothered about balancing the load, or is that the one thing they leave to the discretion of the electrician?