Hello, well let's open the floodgates.
Let me say first off, over here our 10A socket outlet circuits are protected in accordance with the size of the cable that feeds it, for a 1.5mm2 circuit, it is protected at 16A max, if it is wired in 2.5mm2, the maximum size of MCB that may protect this is a 20A, by regulation, you are not allowed to more than double the size of the outlet, with the protection.
With respect to smaller appliances in kitchen areas, they are normally fed through the normal socket-outlet circuits, as the MCB protection is the same for all appliance circuits, apart from Cookers,etc.
Hutch-All of the new types of accessories over here are like this,it is what we call a clean look, however with respect to the ID plates, these are more convenience than anything, it makes life a lot easier in a large installation working out which board and CB feeds which socket/light switch.
(Check out hpm.com.au or pdl.co.nz)
Our electrical equipment over here, must be able to withstand a continuous voltage of 245VAC,it is only in rural areas that the voltages, vary a wee bit, as we have ATC units(Auto-Tap-Changers),to set our voltage within 2.5% of the nominal voltage(230V).
With respect to colour codes in our flexes,
the colour code was changed some years ago, to combat the problem with DIYers with colour-blindness, getting the Phase and Earth wires around the wrong way, this has killed a few people over here.
We now use Brown-Blue-Green/Yellow, as a colour-blind person cannot distinguish between Red and Green.