Would this work? - 02/22/04 06:28 PM
You have an ordinary 120/240V, three wire system with a grounded neutral. Take the two hot wires and place an autotransformer between them. Make this an 120/240V autotransformer and ground the midpoint to a ground rod. No metallic connection with the original neutral. Would this work as a neutral? Or will this only let the smoke out of the transformer?
If you place a load on each leg, will the autotransformer only have to handle the unbalance current?
It seems too good to be true, and that usually means it is...
If you place a load on each leg, will the autotransformer only have to handle the unbalance current?
It seems too good to be true, and that usually means it is...