Posted By: ayrton Load calculations for SDP - 01/03/02 07:34 PM
I need to calculate loads to install a distribution panel fed from a transfer switch.
I have a 200a,
175a
150a
125a breakers all three phase.
None of which the branch circuits draw anywhere near the breaker size. Ineed to put these breakers with their circuits into one panel to be fed from a tranfer switch which of course will be rated accordingly. I know I just don't add these up.
Posted By: Redsy Re: Load calculations for SDP - 01/04/02 02:49 AM
What are the actual loads?
Posted By: Bob Re: Load calculations for SDP - 02/06/02 05:47 PM
The size of the breakers does not provide you with the needed information. You need connected load, name plate data from the equipment connected, clip on amp readings on each phase and any other info you can get.
After accumulation of the information you can make a decicion as to what size equipment you will need. Add 25% for future load. Its possible that the old load has been removed and the present breakers size
is not required

[This message has been edited by Bob (edited 02-06-2002).]
Posted By: Scott35 Re: Load calculations for SDP - 02/07/02 04:36 AM
As suggested, you will need to compile Panel Schedule[s] and do a Load Calc [like the NEC Service Feeder load calc].

If you need answers to these items, feel free to post again - leave no details unposted [Linked Image]