Choke Transformer Schematic - 06/19/01 12:38 AM
This connection is similar to the "Boost" transformer, except the relative polarity is Series Subtractive, plus the connection creates a "Choking Effect" on the current that flows through the secondary coil - hence the name "Choke Transformer".
This lowers the voltage, plus limits the current.
The current limiting action is similar to how a Ballast functions [Typical Magnetic Reactor, HX, CWA Ballasts used for HID and Fluorescent lamps].
Maximum output current is based on the secondary winding's ability to create current, so the short circuit current would be what ever the secondary coul can produce [same as the reactor type Ballast].
Total KVA that can be drawn through the secondary is figured same as any other Buck/Boost transformer - % of Pri/Sec voltage
Example: 120 x 12 VAC - 1 KVA = 1000% of 1 KVA , or 10 KVA max.
Another example: 240 x 12 VAC - 1 KVA = 500% of 1 KVA, or 5 KVA max.
Hope everyone likes these schematics!!
Any comments???
Scott SET
[This message has been edited by Webmaster (edited 06-18-2001).]