Posted By: renosteinke Burned Switch - 07/23/07 08:04 PM
Picture submitted by Waymag. He'll fill in the details:

[Linked Image]
Posted By: ShockMe77 Re: Burned Switch - 07/23/07 11:53 PM
Lightning?
Posted By: waymag Re: Burned Switch - 07/24/07 12:26 AM
We still do not know what made this switch have a melt down. It was on a 277volt circuit and the breaker never tripped. The breaker was a Cutler Hammer Power Line c style breaker. This is also a code violation type deal because 120 and 277 were in the same box. I know the contacts inside the switch had welded together.
Posted By: electure Re: Burned Switch - 07/24/07 12:40 AM
The 120V switch and 277V switch can be in the same box IF the voltage between 2 adjacent switches doesn't exceed 300V.

It's in 404.8(B) smile

(I wonder what the voltage between the 2 systems is?)

Posted By: renosteinke Re: Burned Switch - 07/24/07 01:21 AM
Perhaps the switch was not rated for 277?
Posted By: pauluk Re: Burned Switch - 07/24/07 02:45 PM
Originally Posted by electure
(I wonder what the voltage between the 2 systems is?)


Best case = 157V, worst case = 397V, depending upon phasing.
Posted By: electure Re: Burned Switch - 07/25/07 12:55 AM
My, how simple! laugh
Posted By: waymag Re: Burned Switch - 07/25/07 01:12 AM
Well it had 120v and basically 480v too because the other 2 switches were 277 on a phase and 277 on b phase... 1-120v switch and 2-277 volt switches...after repullint wire back up to j box I did an amp reading and got 4 amps on the 120v switch 3.5 on one of the 277 volt switches and 1.5 on the other 277 volt switch.