Picture from Norcal:


[Linked Image]
ASSuming that this is an outdoor installation:

Disconnect not 3R rated
Greenfield not acceptable in wet location.
Receptacle below disconnect not wet location type, no cover.
Panel on left appears to have pipe plug installed in top hub, rather than proper closeoff plate.
Interesting claim that 'Greenfield' (flexible metallic conduit) is not allowed in wet locations

Are you sure? After all, MC is allowed in wet locations.

As for the receptacles .... would their being located under the larger boxes make those 'damp,' rather than 'wet' locations?

This pic also suggests two other issues.
The first is the matter of lock out / tag out. It looks to me that the disco is old enough (pre-1990) that you may not be able to lock it out.

The second is the surface that everything is mounted on. How do you mount stuff to sheet metal walls - especially when you don't have access to the other face?
Posted By: iwire Re: What's wrong here? Disconnect Installation - 05/20/07 06:20 PM
Originally Posted by renosteinke
How do you mount stuff to sheet metal walls - especially when you don't have access to the other face?


It depends on what I am mounting.

If it was lightweight I might use a #12 sheet metal screw.

Than I may move to toggle bolts.

Move up again with unistrut and toggles or uni-strut tec-screwed into the building structure under the tin.

Assuming the FMC contains type "W" conductors it would be allowed.

Strangely IMO the liquid tight flexible metal conduit is in violation of 225.22
Well, the greenfield might be acceptable if THWN conductors are used, AND if arranged in such a way as to prevent water entry into enclosures. I personally like to avoid installations that require a "judgement call" on the part of the AHJ, and just use sealtite outdoors.

There was nothing said about lack of access to the opposite side of the wall. Properly securing stuff would be pretty difficult then. MAYBE toggle bolts might have a chance, but I wouldn't really trust them.
Life is seldom cut & dry. I posted this pic here, rather than in "violations,' as it brings up so many things we can discuss!

For example, I personally would not use Greenfield in this application ... but, the NEC does not clearly say "no."

For example ... that pipe plug ... I've never seen an "electrical" one, and I've encountered a few such cans that did not use common plates .... and the maker has long since gone away.
Otherwise, several makes of these boxes require you to have access to the inside to attach a blank plate. Personally, I'd just as soon folks keep their mitts out of such boxes ... so I'd just as soon see them use a plug, than leave it open.
Originally Posted by iwire

Strangely IMO the liquid tight flexible metal conduit is in violation of 225.22


Could you please explain this? I'm not in disagreement with ya, just trying to understand. Does it have something to do with the "shall be arranged to drain" vernacular mentioned in 225.22?
This is the same building as the where the single phase device was being used to supply a 3 phase welder,if you saw inside the switch you would really have a fit w/ all the double lugging and the paper wasp who has made its home inside.

Note to John, that switch can be locked out with no problems.
Decided to add some more details, this building is about 3 years old and is on a farm,being agricultural, requires no inspections.
Thinking here...I wonder what's on the inside of these two enclosures??

Disco feeds panel? Panel feeds disco? without seeing the interiors, no clue.

Looks like a feed thru...three raceways into the disco (and a receptacle) Two raceways into 'panel' (and a receptacle).???

Inside or outside? NEMA3 panel, NEMA1 disco.

Flip cover on left device, raised 4" or 5" on right device, interesting.. an in-line GFI on the cord. The greenfield? what's in it?? "w" conductors, OK, but not something this guy would use.

'Nuff said for now.

John
Posted By: yaktx Re: What's wrong here? Disconnect Installation - 06/04/07 11:12 PM
Originally Posted by HotLine1
Disco feeds panel? Panel feeds disco? without seeing the interiors, no clue.


Wanna bet the hots are in the conduit, and the neutral is in the greenfield, or something else so outrageous?
Posted By: yaktx Re: What's wrong here? Disconnect Installation - 06/04/07 11:19 PM
Originally Posted by NORCAL
Decided to add some more details, this building is about 3 years old and is on a farm,being agricultural, requires no inspections.


Oh yeah, and as everybody knows, no inspections means no Code, right? Wish I had a dollar for every time I heard that one!
Norcal:
Where are there 'no inspections' on agr. properties??

John
During one jobsite visit, I told the Contractor that he had violated the maximum number of bends in a set of 4" conduits.
He told me that since it was for the phone cables, the Code didn't apply. The Code ONLY applied for power wiring.

By a happy coincidence, the local AHJ was on site the same day and was in earshot of that remark.

It was amazing how fast that conduit got ripped out and a pullbox installed. Sometime all it takes with some folks is a gentle crack on the head with a redtag.