Mike (mamills)
I have a question about that 400a. disco. Shouldn't there be more than just the bus duct to support something that large (i.e., some kind of support from the back of the box directly to the wall)?
Mike I have never seen one that required additional support or recommend it. This is actually shallow for a 400 amp fused bus duct disconnect. I would expect one today to be at least a 12" deep not 6"(?) like these ones.
The switch grabs the bus duct in 4 places, it is very rigid, the bus duct is bolted to each floor it passes though through a series of springs to compensate for expansion / contraction. Mounting the switch to the wall would defeat the reason for the springs.
We usually use flex for the connection to a bus duct switch.
The metal nameplate is definitely upside down, so it's quite clear that the boxes are. The inside door label in the 3rd photo confirms that. And there are the inverted mounting keyholes.
Actually the metal name plate is right side up,
and that is impressive as is is on with rivets, not nuts and bolts like a I would expect in a 'field modification'.
Another 'impressive' job was the use of a wireway 'ell' in place of a conduit body or bend.
This was repeated 3 or 4 times, besides the fact the wireway should be supported and it is just plain ugly work I know I would not have enjoyed getting the four 500 or 600 Kcmil copper conductors into that fitting.
Bob