Posted By: Admin Weathered Weatherhead - 10/19/04 03:54 AM
Quote
We found this one by accident, I looked up to see if we needed to replace the wires and found them in poor shape speaking mildly. after taken it down (with power turned off) we found that a couple of the strands of the netural had burnt into because of contact with one or both of the lines.

- Jwww
[Linked Image]

[Linked Image]

[This message has been edited by Webmaster (edited 10-18-2004).]
Posted By: Dave55 Re: Weathered Weatherhead - 10/19/04 09:35 PM
From the pictures it looks like way too much wire crammed into too small a conduit and service head. Do you know the wire ga. and conduit size, Jwww???

Dave
Posted By: Jwww Re: Weathered Weatherhead - 10/20/04 02:32 AM
The conduit was 2" and the wire was 4/0.
Posted By: e57 Re: Weathered Weatherhead - 10/20/04 03:46 AM
Would not even think of disturbing that.
Posted By: Ryan_J Re: Weathered Weatherhead - 10/20/04 01:23 PM
It reminds of the Pink Floyd The Wall movie with the cartoon meat grinder.
Posted By: Trumpy Re: Weathered Weatherhead - 10/20/04 01:52 PM
LOL Ryan,
I had exactly the same thought!. [Linked Image]