Posted By: Admin Panelboard & Service Violations - 07/22/04 06:09 AM
(submitted by Joe Tedesco)
Quote
(picture 1) shows a 208/120V panelboard, typical of panelboards throughout the building. In addition to other violations, notice that the panel is not grounded, that neutrals and grounding conductors are freely mixed on the neutral bus, multiple-colored insulations on neutral bus, white used as a phase conductor in feeder, etc.
[Linked Image]
Quote
(picture 2) shows a Fernco plumbing coupling used on the service conductor raceways between a pad-mounted transformer and the service entrance switchgear. This is a 1200A 480V service.

Enjoy

Robert E. Brown
[Linked Image]
Posted By: electure Re: Panelboard & Service Violations - 07/22/04 12:04 PM
It's a pity that whoever did this must have known better, (note the Touch-Plate relay) but just had no ethics.
It looks like someone pulled the feeder as a 1Ø, and then, when they realized that it was 3Ø, just tried to make it work.
This job stinks.
Posted By: pauluk Re: Panelboard & Service Violations - 07/22/04 12:15 PM
Quote
It looks like someone pulled the feeder as a 1Ø
As in thinking it was a 120/240V panel? Sounds plausible from the feeders there. I don't know how long that feeder is, but how hard would it have been to just pull in another blue conductor and do the job properly? [Linked Image]

Any idea what that transformer on the top of the panel is feeding? And what's that gizmo to the right of it?

Even if the xfmr secondary is low voltage, the open wirenutted splices outside the panel are still very messy and I don't think much of the mounting and wiring method.



[This message has been edited by pauluk (edited 07-22-2004).]
Posted By: Lostazhell Re: Panelboard & Service Violations - 07/22/04 04:21 PM
Scott,
That would be my guess also... The plumbing fitting is a nice touch! [Linked Image]
Pauluk,
The gizmo is a "Touch-Plate" relay.. Typically we find these in a pull can with about 20-30 other ones & a transformer to power them.... I've seen these things used here & there for all the switching in a house.. (Usually, a frustrated customer is asking to get rid of it!) Here's a link to their site... For the longest time, I thought they were out of biz.. I was wrong! http://www.touchplate.com

-Randy
Posted By: electricman2 Re: Panelboard & Service Violations - 07/22/04 11:43 PM
If this is a 3phase panel then the green wire is being used as the grounded conductor, right? I like the set screw coupling on top too, the pipe must hav been a little short. [Linked Image]
Posted By: classicsat Re: Panelboard & Service Violations - 07/24/04 01:38 AM
Touchplate looks like a new version of those GE home control systems from the 1950s.
Posted By: electure Re: Panelboard & Service Violations - 07/24/04 01:49 AM
Touchplate was a competitor with those old GE systems. They've been around a long time.
Go check out a new GE LV lighting control, and you'll see they use the same relays as they used then.

Touchplate has a ratcheting relay that advances on-off etc, each time it's given a signal from the momentary switch, so it only needs 2 wires to connect it.
The GE's need separate on and off signals from the switch, so require 3 wires.