Posted By: Admin This Used To Be A Conductor - 05/24/04 06:52 PM
This Used To Be A Conductor
Photos by Dave55:

[Linked Image]

[Linked Image]
Posted By: resqcapt19 Re: This Used To Be A Conductor - 05/24/04 07:03 PM
Is that an aluminum conductor that was installed underground? That's what normally happens to aluminum if there is a small nick in the insulation and the conductor is installed underground.
Don
Posted By: Dave55 Re: This Used To Be A Conductor - 05/24/04 07:30 PM
Exactly, Don.

Dave
Posted By: Lostazhell Re: This Used To Be A Conductor - 05/24/04 11:44 PM
Ahhh, this looks very familiar! I once had a call at a mobile home park where about 8 units had no power... A month earlier a plumbing company installed a sewer cleanout near one of the affected units.. All the utilities in this place were in the same trench.. Tone traced it & lost signal right next to the cleanout.. Lo & behold I found direct burial #1 Aluminum conductors just like this there... I wonder if the plumber noticed a tingling feeling when he was doing his work? [Linked Image] The circuit breaker controlling this did not trip (Zinsco 90A 240V)..

-Randy
Posted By: electure Re: This Used To Be A Conductor - 05/25/04 12:10 AM
What causes the white "globs" on conductors that get wet?
I've seen this many times, but never knew why the formed....S
Posted By: SvenNYC Re: This Used To Be A Conductor - 05/25/04 03:47 AM
I think the white crud is aluminium oxide....

Aluminium reacting with the oxygen in the water and probably who knows what else in the soil?

Just a guess....I'm no chemist. [Linked Image]
Posted By: Mean Gene Re: This Used To Be A Conductor - 05/25/04 04:12 PM
I think the electricity in the conductor has a lot to do with it also.

Where's Scott35 ?? Surely he could give us an indepth explanation of this occurance.
Posted By: crash Re: This Used To Be A Conductor - 05/26/04 04:04 AM
SvenNYC: I'm no chemist either, so I phoned one up. The white crud is aluminum oxide.

[This message has been edited by crash (edited 05-26-2004).]
Posted By: Trumpy Re: This Used To Be A Conductor - 05/26/04 11:00 AM
To agree with Crash,
That is Aluminium Oxide, caused by fresh Aluminium being exposed to Oxygen.
Water only accelerates the deterioration of the Aluminium metal below, the oxide surface. [Linked Image]
Posted By: Bjarney Re: This Used To Be A Conductor - 05/27/04 02:45 AM
For aluminium conductor, air and moisture readily form oxides and hydroxides when in contact with the metal on its exposed surfaces—coincidentally happening to be superb {and merciless} insulators.

As is probably evident from the images, in time the oxides also migrate into cable-strand interstices.

Nonreversible tool-compressed terminations and splices are unbeatably durable for many decades of electrical-connection reliability [and survival of the electrical system.]