Posted By: Admin Is this Mast properly supported? - 08/24/03 12:44 AM
[Linked Image]
Quote
Is this mast service properly supported? Shouldn't there be additional support? (230.28?)

-richard
Posted By: electure Re: Is this Mast properly supported? - 08/24/03 01:40 AM
I think the term "adequate strength" is subject to interpretation.
Another item in 230.28, though, is not.
"Only power service-drop conductors shall be permitted to be attached to a service mast."
The phone and cable TV(?) wires have got to go...S
Posted By: pwood Re: Is this Mast properly supported? - 08/26/03 08:46 PM
poco in this area requires a guy or brace when mast exceeds 3' over roof.it also considers the length of the conductors and any strain on the mast.
Posted By: Bill Addiss Re: Is this Mast properly supported? - 08/26/03 09:16 PM
Our POCO requires a minimum of 32" between supports and if mast extends more than 5 feet above last support it must be 3-1/2" Galv pipe.

Bill
Posted By: Redsy Re: Is this Mast properly supported? - 08/27/03 11:16 AM
Are those one-hole straps that are securing it to the building?
Posted By: Admin Re: Is this Mast properly supported? - 08/31/03 08:05 PM
[Linked Image]
Quote
I took closer look and found the clamps to be bolted .
the last clamp is 16 inches from the roof, and the 10 foot mast is 5 feet from the top of the meter to the top of the roof.

-richard