Posted By: Admin 200A Service and SubPanel - 09/16/02 01:04 AM
Forwarded by Joe Tedesco:

[Linked Image]

[Linked Image]
Quote
Here is a picture of my outside 200 amp service panel and inside sub panel. There were no violations on this inspection.

Jerry Gilley
Posted By: sparky66wv Re: 200A Service and SubPanel - 09/16/02 03:46 AM
I hate to be nit-picky, but the GRC nipple could be argued to be a violation of 250.6(A) and it appears that 250.92(B) may be violated if the KO's have any eccentric or concentric rings left on the box where the nipple is connected (and assuming there is no bonding bushing in the meterbase that I wouldn't be able to see).

PVC will solve both problems in the future.

That's one that I learned raht-cheer on ECN!

(Thanks Bill)
Posted By: sparky66wv Re: 200A Service and SubPanel - 09/16/02 03:49 AM
Actually, I lied...

I LOVE to be nit-picky!!!

[Linked Image]

Not a violation, but, no 40 space MLO's?

[This message has been edited by sparky66wv (edited 09-15-2002).]
Posted By: Bill Addiss Re: 200A Service and SubPanel - 09/16/02 04:04 AM
What do you think about the 200A sub (w/main) being fed from a 100A breaker?

Bill
Posted By: sparky66wv Re: 200A Service and SubPanel - 09/16/02 04:23 AM
I suppose as long as the lugs on the Main Breaker and the Neutral and EGC Lugs are rated for the size of wire used, it still offers a convenient "bus disconnect" and the 22KAIC protection.

Plus, like here, a 200A 30 or 40 space MLO may be actually more expensive and require a special order!

Not a code violation, but my PoCo requirements would want the straps on the mast within 12" of the meterbase (minimum 30" spacing and within 12" of the weather head).

[This message has been edited by sparky66wv (edited 09-16-2002).]
Posted By: caselec Re: 200A Service and SubPanel - 09/16/02 05:39 AM
Why are there white wires connected to the circuit breakers without re-identification? The breaker in the upper left corner of the main panel looks like a Siemens not GE. Most of the cables in the main panel appear to enter through 1 KO and I have never seen a connector listed for more the 4 cables. The main lugs on 200 amp GE load centers are listed for min. #1 conductors and the wires feeding the sub panel look smaller but its hard to tell with this picture.
Posted By: sparky66wv Re: 200A Service and SubPanel - 09/16/02 05:44 AM
Wow, I missed all that at first...

I've got to go to bed...

(Note time of post)

Oh, to add... Just a hunch, but the service entrance neutral connected to the top lug of the meterbase and the service feeder neutral appears to have been stripped from a piece of SER (going by the white stripe). I would think that THWN or RHW-2 or the like would be required here.

[This message has been edited by sparky66wv (edited 09-16-2002).]
Posted By: Redsy Re: 200A Service and SubPanel - 09/16/02 11:15 AM
Is that rigid nipple OK between the meter socket & panel? Should it be a Meyers hub?
The GEC connection is made at the meter socket. I believe our PoCo forbids that.
Also, although not a violation, see my post about excessive NM jacket in the panel.
Posted By: txsparky Re: 200A Service and SubPanel - 09/16/02 05:05 PM
Is there a connector on the egc at the meter or is it routed through 1/4 inch k.o? [Linked Image]
Posted By: sparky66wv Re: 200A Service and SubPanel - 09/16/02 05:32 PM
LOL at txsparky.... You're a bad man!

[Linked Image]

Redsy, yep, that's what I was getting at with the GRC Nipple violating 250.6(A)for parallel current paths and perhaps 250.92(B)for a lack of bonding bushing.

I still can't believe I didn't see all those white conductors before!

[Linked Image]
Posted By: daniel damon Re: 200A Service and SubPanel - 03/06/03 01:06 AM
they forgot to put a recpt at the end of that hanging wire to the right
Posted By: rhagfo Re: 200A Service and SubPanel - 03/06/03 02:27 AM
If that is a 200 amp,sub the wire feeding looks to be a little small, it is copper, but it looks like either there is a lot of potential load on that sub, or each outlet has it own breaker. I also wonder about the feed from the meter base. It looks like striped down SE cable, bare ground.
Posted By: Electricmanscott Re: 200A Service and SubPanel - 03/06/03 01:12 PM
Ty wraps in panel===pain in the a**!
Posted By: resqcapt19 Re: 200A Service and SubPanel - 03/06/03 04:16 PM
sparky66,
Are you trying to tell us that you can't use metallic raceways for a service?

Redsy,
I see no reason for a sealing hub where a raceway enters a raintight enclosure below the electrical equipment within the enclosure. Some utilities require that the GEC be landed in the meter can.

Don
Posted By: Foghorn280 Re: 200A Service and SubPanel - 03/10/03 05:18 PM
Shouldn't the grounded conductor be identified?