Posted By: Admin What's wrong with this Picture? - 12/08/00 03:26 AM
<p align="center"> <img border="0" src=&q...uot;300" height="200">

Click on Photo for a closer look
<p align="center">Note: Wirenuts were removed and are not part

of the violations under scrutiny here.
<p align="center">Comments?
Posted By: sparky66wv Re: What's wrong with this Picture? - 12/08/00 05:24 AM
To start off with...

11 #12 Conductors in a box designed for 6 (assuming the box is 1-1/2" deep and not 1-1/4") Including the deduction for the clamps, there are 6 too many conductors in the box.

The box appears to be unsupported.
Scratch that... I see the bracket now...

The ground wires should be snipped off IF there is no "true" ground present in the box...OR if one of the 12-2-G wires is the feeder, the box isn't bonded properly.

The conductors do not have six inches of free length.

Are the cables stapled within 12 inches of the box? Doubtful, but inconclusive in the photo.

Less than 1/4" of jacket on th NM Cable in the box... (Some one told me that rule is only for plastic boxes...any comments?)

No Connector on the ground? (Crimp or wirenut) You did say that the wirenuts were removed, but the "ground" conductors don't appear to have the scars. (This same someone told me that twisting the grounding conductors together with no other means of connection is ok by code...sounds fishy to me...)

Was this protected at 15A or 20? There is one lone #14 Cable I believe...

That's about all I see...
Posted By: Bill Addiss Re: What's wrong with this Picture? - 12/08/00 12:43 PM
Sparky,

Thanks for your Comments. There is at least 1 more thing that is fundamentally wrong here that you didn't see (Well, you did but you didn't realize it)

To Comment on your other Comments, they are pretty good. The location is in a basement so it may have been a porcelain fixture location at one time. I never heard the 1/4" jacket rule only being for plastic boxes unless they mean that it should be longer in other boxes such as this with clamps in which case I would say that the jacket should extend 1/4" further than the clamp. Maybe someone else has a comment on this?

Can you see anything else? [Linked Image]
Posted By: gpowellpec Re: What's wrong with this Picture? - 12/08/00 07:58 PM
Are the clamps upside down?
Posted By: resqcapt19 Re: What's wrong with this Picture? - 12/08/00 09:20 PM
The white jacketed cable on the left in not correctly installed in the clamp, and I don't think you are permitted to place more than one cable under a single clamp.
Don(resqcapt19)
Posted By: Bill Addiss Re: What's wrong with this Picture? - 12/08/00 11:19 PM
Don,

You are probably right about the clamps. Do you know why they are shaped like they are though?

What I am looking for is something that is not only wrong, but it is totally the opposite of what it should be. (that's a hint)
Posted By: Admin Re: What's wrong with this Picture? - 12/10/00 08:22 AM
Ok,

Here's another.. Hmm what was the name of that Chubby Checker song?
Posted By: sparky66wv Re: What's wrong with this Picture? - 12/10/00 04:24 PM
The neutral wires are twisted in the wrong direction... (counter-clockwise). For that matter, I guess the hot wires were too.

Are the clamps designed for BX or other Cable?
Posted By: Bill Addiss Re: What's wrong with this Picture? - 12/11/00 12:14 PM
Sparky,

Ding Ding Ding !! You got what I was looking for! I guess the Chubby Checker mention must have done it. When this box was opened the wirenut just about fell off the white wires. This occurrance is often accompanied by having tape wrapped around to hold it on.


The clamps came with the box I'm sure. I was wondering myself why they are shaped like they are and if a wire was allowed to be installed as the newer one on the left seems to be. I can see an advantage to putting the cable in this way if say an extension ring was added it would be easier to reach the wires. I don't think that the clamps are designed for Bx because there is no provision to retain the anti-short bushing on the cable. [Linked Image]
Posted By: LNP&S Re: What's wrong with this Picture? - 12/29/00 11:23 AM
Bill
As I remember some of these older boxes had the "romex" knockouts in the top as well as in the side allowing installation on the bottom of a floor joist and entry through the top of the box. I think the clamps were designed to accept cables either through the top or side knockouts - thus the rounded cable formations on top and side of the clamp.
Posted By: Tom Re: What's wrong with this Picture? - 01/01/01 04:45 PM
Here in WV, this must be considered a state of the art junction box since I've seen so many just like it, or their close cousins.

By the way, just in case you can't see it, my tongue is firmly planted in my cheek.

Happy New Year to all.

[This message has been edited by Tom (edited 01-01-2001).]
Posted By: sparky66wv Re: What's wrong with this Picture? - 01/01/01 07:50 PM
Yeah, I can vouch for that, Tom! It seems to be the standard J box for these parts; and you are allowed to put as many cables as you can force into it as well!
Posted By: sparky66wv Re: What's wrong with this Picture? - 01/15/01 08:44 AM
Quote
Originally posted by Bill Addiss:

I never heard the 1/4" jacket rule only being for plastic boxes unless they mean that it should be longer in other boxes such as this with clamps in which case I would say that the jacket should extend 1/4" further than the clamp. Maybe someone else has a comment on this?


Found an article by Charles R. Miller in the ECM Code in Focus. He points out that the 1/4" rule is in the section for NM boxes. In order to keep from plagiarizing, you can read it <a href="http://www.ecmag.com/backsearch/">here</a> and search under September 2000 Author Charles R. Miller.

Notice by the number of edits, I tried to make it easier...

Like the AC anti-short bushing and the anti-oxidant "rules", I wonder what other "codes" don't really exist?


[This message has been edited by sparky66wv (edited 01-15-2001).]

[This message has been edited by sparky66wv (edited 01-15-2001).]

[This message has been edited by sparky66wv (edited 01-15-2001).]
Posted By: exxon Re: What's wrong with this Picture? - 02/05/01 05:36 PM
Would also have been nice to see the 150mm of free conductor left in the box for splices , But I guess he wasn't finished running wires into the J.Box as he need the room . [Linked Image]
Posted By: electure Re: What's wrong with this Picture? - 03/06/01 02:48 PM
Those codes for anti-shorts, etc. do exist.
see 110-2, 110-3, 90-7. Installation to manufacturers specs. The cable I get comes with a bag of bushings attached right to it.