Posted By: Admin Re: Fixture Support - 03/24/09 01:58 AM
Quote
Hi—
Found on the roof of a local starbux; it all sits on a TB supported by a piece of ˝-inch EMT...

They look like a pair of 500W quartz-halogen fixtures.

How would you "bring this up to code"?

—busbar

[Linked Image from electrical-photos.com]
Posted By: renosteinke Re: Fixture Support - 03/24/09 02:41 AM
Just where is the violation?

OK, maybe there's a fill issue in the conduit body ... but using a Bell box would not change the support issue one bit.

The fixtures arefairlylightweight, and the length of the mast isn't very much.

Cheap? Schlock? Absolutely- but I think it meets code.
Posted By: electure Re: Fixture Support - 03/24/09 03:51 AM
It's a violation of the support required by 314.23(F).
Posted By: renosteinke Re: Fixture Support - 03/24/09 06:01 AM
Good catch, Electure! So.... rigidis OK for this use, but not EMT.
Posted By: ghost307 Re: Fixture Support - 03/24/09 02:38 PM
Is there anough room inside the T to legally make up the splices?
Posted By: packrat56 Re: Fixture Support - 04/05/09 04:39 AM
I agree ghost307, that's a good question.
Posted By: mxslick Re: Fixture Support - 04/21/09 10:24 PM
As long as you don't exceed the fill percentage of the fitting, you can make splices in them. I can't recall the Code section offhand though...

I have seen splices in T-fittings before, they seem to fit ok without too much drama.
Posted By: mikesh Re: Fixture Support - 04/21/09 10:56 PM
some conduit bodies are approved for a splice some are not and I don't know the differences.
Posted By: frenchelectrican Re: Fixture Support - 04/22/09 05:57 AM
If they have the CU IN stamped inside the TB conduit body then yeah it can be used for splices otherwise no it can not be used for splices but I know some guys do used the oversied TB bodies for it and install the reduced bushing in there to make room for splices.

Merci,Marc
Posted By: leland Re: Fixture Support - 04/22/09 03:59 PM
I've used the 'over size' method a few times.mainly for parking garage light retros'