Posted By: electure Not Spectacular - 09/08/06 11:17 AM
No smoke, no fire.
I had to test the photocell, and just happened to open the box. The bottom conduits run underground to an ATM machine about 100' away. All the power circuits are 120V.
How many violations are there here?


[Linked Image]

(BTW, this job passed inspection)

[This message has been edited by electure (edited 09-08-2006).]
Posted By: techgod Re: Not Spectacular - 09/08/06 03:17 PM
At least the installer maintained the minimum bending radius for the Cat 5. [Linked Image]
Posted By: LarryC Re: Not Spectacular - 09/08/06 06:08 PM
I like the Cheshire cat neutral coming out of the wire nut. (Slowly fades away until nothing is left)

Larry
Posted By: iwire Re: Not Spectacular - 09/08/06 09:23 PM
Larry the white that 'vanishes' actually dives down the left hand 1/2".

Looks like a hex head Tek screw holding the grounding lug.

The paint was not cleaned off at the grounding lug.

There are two conductors in a terminal that is rated for one (IMO)

The neutrals look less than 6"

That group of funny blue cables might be better off in a separate enclosure.

And it's missing the cover. [Linked Image]
Posted By: CaOperator Re: Not Spectacular - 09/09/06 12:27 AM
Oops just reread, the post, it is a photocell, lol.


[This message has been edited by CaOperator (edited 09-08-2006).]