110.11 I think is a stretch, the equipment is listed for outdoor use.
I do not see how you can apply 110.26(F)(2) to this outlet, if you do you will also have to apply all sections of 110.26 to all outlets and switches.
This would make kitchen counter outlets a violation of the work space requirements for example.
You defiantly got me with 314.15(A)
, IMO that is right on the money, I will not forget that section now, Thank you.
300.6(B)
Allows boxes to be in direct contact with the earth "where made of material judged suitable for the condition, or where provided with corrosion protection approved for the condition."
Around here Bell boxes are judged suitable for dirt water etc.
I guess that is an AHJ call.
I agree red tag with 314.15(A) on it.
Bob