Here's a (name removed) utility job - NOTE 13kv riser cables up against streetlight lumiare.
Jay Anderson
(submitted via Joe Tedesco)
Ok my line or outside experiance is limited.... But is the pole too short? Looks like 54'? if thats a 40' there next to it. Secondary and street lighting side too high? Both? Isn't there a rule for seperation of so many feet? Any of the linemen out there got comments for that?
Am sure they should not be wrapped around aech other like that...
doesn't look like there is any type of bushing on that riser.
Who has to service that cobra-head light fixture?
Not me...
Utility systems are often designed and installed under the
National Electrical Safety Code, published by IEEE.
[In California, the document is
General Order 95 for overhead systems, at
]www.cpuc.ca.gov/Published/Graphics/13352.PDF]