Posted By: Joe Tedesco Angle or U Pulls, How Many Wires? - 06/16/02 11:58 AM
[Linked Image]

Please review the NEC for possible violations here.

Question: Does the NEC allow the use of this method with "how many" wires in a 3 inch EMT?
Posted By: Gwz Re: Angle or U Pulls, How Many Wires? - 06/16/02 05:48 PM
Probably for a two conductor telephone jack.

[This message has been edited by Gwz (edited 06-16-2002).]
Posted By: resqcapt19 Re: Angle or U Pulls, How Many Wires? - 06/16/02 07:36 PM
If this is a Chapter 8 installation, there is no box size requirement in the code. If it is some other system with wires larger than #6, it appears to be a violation of 314.28(A). The number of wires is only limited by the wire fill rules in Table 1 of Chapter 9.
Don
Posted By: elektrikguy Re: Angle or U Pulls, How Many Wires? - 06/17/02 12:45 AM
Too True GWC. Maybe they had a whole bunch of 2 inch left over at the end of the job and used it instead of 3/4?
Posted By: Gwz Re: Angle or U Pulls, How Many Wires? - 06/17/02 03:10 AM
elecktrikguy,

I was being sarcastic.

Always 4" RMC required for the telephone and then a quad #22 conductor is installed.

I'm with Don's comment.