Posted By: Cinner Sharing a neutral - 06/01/11 02:56 AM
On a 3 phase panel - if 2 circuits share a neutral - do you have to use a 2 pole breaker so that if one trips they both trip?
Posted By: twh Re: Sharing a neutral - 06/01/11 05:47 AM
14-010. It depends on whether the circuit feeds lights or plugs.

It isn't a trip issue, though. We can still use fuses as long as we include a disconnect that meets the requirements of 14-010(b).
Posted By: Cinner Re: Sharing a neutral - 06/01/11 05:57 AM
It is for receptacles. Can you use 15 amp single pole breakers if the neutrals are being shared to more than one circuit?
Posted By: jay8 Re: Sharing a neutral - 06/01/11 04:30 PM
the trade practice for three phase 4 wire circuits feeding 120/347 volts loads is single pole breakers. I could see good justification for a three pole breaker to ensure a circuit is completely disconnected included any current on a shared neutral but I dont think any code rule requires it. If the receptacle/load is using more than one phase then you need to use 2 or 3 pole breaker.
Posted By: jay8 Re: Sharing a neutral - 06/01/11 08:30 PM
and before a bunch of posts come about the implications of common breaker handle for single phase loads, I can see some change in installation practice that will reflect the issue of current on shared neutral - such separate neutrals etc