Posted By: jay8 AFCI breakers - 06/25/09 04:09 AM
FYI,I just noticed Siemens has put out a two pole AFCI breaker, I am sure the other manufacturers will follow. It was the first I had heard of this.
Posted By: Check Pilot Re: AFCI breakers - 06/27/09 06:04 AM
Hey jay8, can you post a link or something??. I've been looking for about a hour now and don't see it.

Thanks.
Posted By: canuck Re: AFCI breakers - 06/27/09 11:25 PM
Here's a link to the siemens webpage:

http://www2.sea.siemens.com/products/residential-electrical/afci
More Details:
http://www2.sea.siemens.com/Products/Residential-Electrical/AFCI/2_pole_+Combination_Type_AFCI.htm

Appears that Eaton has one aswell:
http://downloads.eatoncanada.ca/dow...20Guide/Fire-Guard%20-%20SA00402001K.pdf
Posted By: canuck Re: AFCI breakers - 06/27/09 11:56 PM
Here's Schneider's info concerning shared neutrals and AFCI's:
http://ecatalog.squared.com/pubs/Ci...rrupters%20%28AFCI%29/0760DB0203R902.pdf
more at:
http://arcfault.ca
Posted By: jay8 Re: AFCI breakers - 06/28/09 06:14 AM
sorry, forgot to include a link, thanks to canuck for taking care of business.
Posted By: Sandro Re: AFCI breakers - 07/01/09 04:40 AM
2 pole has been available for at least 2 years now in the Cutler Hammer line.

Posted By: mikesh Re: AFCI breakers - 07/02/09 07:00 PM
I am wondering what would require a 2 pole AFCI? I can't think of any branch circuit that requires it. Maybe the latest NEC has a few? Nothing mandatory in the CEC.
I am not saying there are no good or rational reasons for an AFCI 2 pole branch circuit just nothing in the code requiring one.
Posted By: renosteinke Re: AFCI breakers - 07/02/09 08:11 PM
I am not aware of how the Canadian codes treat what we call "multi-wire branch circuits,' or, less formally, 'shared neutrals.'

This is the practice of running a three wire cable from the panel to the first junction box, where the two circuits are separated. Thus, they both use the same neutral for the final run back to the panel.

For such a circuit, the GFCI or AFCI breaker must, necessairily, control both of the 'hot' wires; thus the need for a two-pole breaker.

Here the more current issue relates to a design change in the AFCI's themselves .... no point opening that can of worms here!

It's also not unusual for the room air conditioner or baseboard heat to be a 240v circuit.
Posted By: mikesh Re: AFCI breakers - 07/06/09 07:01 PM
Yes we do have multi wire branch circuits as you describe but if I was doing it I would not use a 2 pole breaker since the cost is more than double a 1 pole. For GFCI we generally install a GFCI outlet at the first outlet and seldom use a breaker. IE normal 1 pole breaker and GFCI outlet at the first required location. No common trip is required for a 3 wire circuit unless the devices are on the same mounting strap like as for split receptacles. It is possible to run 2 circuits from 2 X 1 pole CB on different buss with 1 neutral and a GFCI outlet at the first receptacle in each branch. Obviously the neutrals cannot share beyond this point or the service guy will slap someone on the back of the head ;-)
An AFCI circuit requires breaker protection as the entire branch must be AFCI protected. The only outlets required to be AFCI protected are the bedroom Plugs only. No smoke alarms may be on the circuit and lighting may be on the circuit. The cost of an AFCI 1 pole breaker was around CDN $70.00 and 2 pole around $250.00 even for a long home run it is still much cheaper to run 2 circuits.
Posted By: renosteinke Re: AFCI breakers - 07/06/09 08:17 PM
Oh, I won't argue the economics one bit. Indeed, that's been at the heart of the AFCI debate here!

Originally, they were to allow AFCI devices, so you could handle things as you did with GFCI protection. When the requirement actually took efect (1999), though, the code was suddenly re-written to proscribe the devices. Later editions have made devices acceptable under certain restricted situations .... but the device makers have not made the devices available. Once bit, twice shy! For the guy in the field, it remains a puzzle how a 'protection' available in the device costs only $10 extra, while it costs at least $35 additional if the protection is placed in the breaker.

There are any number of reasons why MWBC's are used ... what is worth noting is that our most recent edition (2008) surprised us with numerous new restrictions upon their use. The next edition has several proposals to restrict them even further. Much to my surprise, one breaker manufacturer (Square D) is leading the charge, with a published opinion that MWBC's ought to be eliminated altogether. Personally, I cannot understand why Square D is concerned about this design issue.
Posted By: mikesh Re: AFCI breakers - 07/08/09 01:13 AM
MWBC was standard in commercial work for ages and still very common but there are still too many guys who just don't pay attention when installing the OC protection. the biggest issue has been damaged grounded circuit conductors (neutrals) typically we always installed the breakers adjacent to each other and labelled the neutral with the circuit numbers. I just don't see this as much and more often than not I am seeing more 2 wire home runs. I suppose harmonic troubles are a huge factor but even that is becoming a smaller problem as the electronics improve their power supplies. IE the power supplied don't dump as much harmonic distortion onto the system.
In the CEC the AFCI device was never even contemplated as we were focused on the installed wiring and not what is plugged into it. Here it is just breakers and so far just for bedroom circuits. If my home panel was big enough I'd install AFCI breakers in all but the kitchen and appliance circuits. Unfortunately my home panel uses all narrow breakers and I don't even have enough space to change the bedroom circuits to AFCI breakers. Why do breakers cost so much more than an outlet that provides the same protection? I don't know as a thermal/magnetic trip breaker in a residential panel is around $10.00 retail. I can't see how the electronics add another $50.00 to the cost.
Posted By: jay8 Re: AFCI breakers - 07/09/09 07:23 AM
The reason I brought the two pole AFCI to attention is primarily for retrofit applications. Consider the residence with a multiwire branch circuit that feeds bedrooms and other spaces.

New construction is a different story.