Posted By: mr_electrician probably a stupid question but....... - 06/27/07 06:36 PM
Hi, I just want to clear the mud when it comes to ground/phase detection lights. When do you need them, and are they needed when the service it is connected to is 3 wire 600V fed from a 4 wire distribution?
Posted By: mikesh Re: probably a stupid question but....... - 06/27/07 11:16 PM
They are required for ungrounded systems. A 240 volt delta secondary for example.
A 600 volt from a wye connected 4 wire secondary requires you bring the grounded conductor to the service box and bond it and ground it. Thereafter you don't need to carry the neutral unless 347 volts is needed. The ground detector lights are not required in the second case as any phase conductor contacting a grounded enclosure will pop a fuse or breaker.