Posted By: GETELECTRIC Conduit Fill - 03/02/07 05:37 PM
Is an insulated ground included as part of your conduit fill.
Posted By: RobbieD Re: Conduit Fill - 03/02/07 05:43 PM
Everything that goes into conduit is considered fill, everything.
Posted By: smokumchevy Re: Conduit Fill - 03/03/07 03:28 PM
Yes, as stated above. See note (3) at the end of Table 6 CEC2006.

-Greg
Posted By: wacked Re: Conduit Fill - 03/25/07 04:33 AM
Can somebody explain the difference between jacketed and non jacketed conductors? With the same voltage rating are they jacketed for more protection or???
Posted By: RobbieD Re: Conduit Fill - 03/28/07 02:22 AM
http://www.nexans.ca/egy/tecdoc/1.htm

This page will give you the answer you are looking for.


Posted By: dougwells Re: Conduit Fill - 03/28/07 02:58 AM
Nice find Rob smile
Posted By: wacked Re: Conduit Fill - 03/29/07 04:42 AM
Thanks Rob, that is exactly what I was looking for!!