Posted By: GETELECTRIC incoming service - 12/13/04 04:57 PM
I have an incoming service 600v 100amp going to a 3 storey commercial bldg, it is being fed overhead, my question is this, can i run the conduit though the parking garage ceiling 50'to the electrical room into the main then into the meter center.Something tells me i can,t but if i do underground from the weatherhead to the electrical room that is ok?
Posted By: crash Re: incoming service - 12/15/04 12:48 AM
That "something" that is "telling you", might be 6-208. Underground is OK but 50 ft through the parkade is not allowed.
Posted By: Tony Moscioni Re: incoming service - 12/15/04 11:11 PM
Where judgement required about "as close as practicable", the following may be used for
guidance on the maximum length of run:

(i) 1.5 m into rooms or areas of combustible construction; or

(ii) 7.5 m into other areas provided:
„h the wiring method is rigid conduit, electrical metallic tubing (EMT) or a cable
with a continuous metal sheath or interlocking armour, (No PVC greater than
625mm2 as per Building Code), and
„h the conduit or cable is mechanically protected where it is within 2 m of the floor.

Tony Moscioni
Electrical Inspector
Electrical Safety Authority