Posted By: shortcircuit Solar PV Wiring Errors - 03/08/13 01:30 AM
There are installers in Mass making errors with the solar array wiring. When using a transformerless inverter such as the Power-One PVI 6000 TL, it is important to wire the solar array as ungrounded or "floating"

This includes:

1. Not using white colored wire in string wiring.
2. Any field installed DC disconnect must break both negative and positive ungrounded conductors.
3. Any string fusing must also be in both ungrounded conductors.
4. Exposed string wiring must be PV type wire.
5. PV module whips must also be PV type wire.

Questions?
Posted By: John_UR Re: Solar PV Wiring Errors - 06/22/14 03:10 PM
I think you should compare all connection diagrams with the following Solar panel installation wiring diagrams with inverter and batteries...
http://www.electricaltechnology.org/2014/06/solar-panel-wiring-installation-diagrams.html

Hope it will help you smile
Posted By: renosteinke Re: Solar PV Wiring Errors - 03/03/24 01:12 AM
The above post links to a site that asks for your credit card before accessing the “free” information. I advise against it.