Posted By: mikeD grounding direct tv - 02/02/10 01:42 PM
Bought house couple years ago .Had direct tv come put coax in 2 of the rooms we hadent moved in yet. Go to house and wire laying on ground blew hole through side of the house theres your free install. Im working on putting all coax under the house comming up in a wall got to looking theres a splice block on the other two rooms with a piece of #12 stuck down in the ground. im fixing all that should that ground be at the dish dont know whats its grounding now.how do you ground coax cable and is it good to do all the coax at the dish just have connectors on them thats all i see.looks like harry home owner install its got to go. and i have holes in my siding but it was free thats what direct tv told me when i called them about it...
Posted By: EV607797 Re: grounding direct tv - 02/02/10 05:33 PM
Just about all COAX splitters and devices contain a grounding lug now. You should just run your ground wire from the first one to the building's grounding electrode. It is not proper to drive a separate ground rod just for the SATV wiring. Don't forget that the dish itself must be grounded as well; not just reliant upon the coax shield. In most cases, the shield never actually comes in contact with the dish at all.
Posted By: gfretwell Re: grounding direct tv - 02/02/10 07:35 PM
The optimum location for your dish is near the service entrance if you can see the satellite from there. Then you have easy access to the ground electrode system with a short grounding conductor. When you are grounding out lightning, the shorter the conductor the better. I would still drive a separate rod for the dish, directly under it and bond that back to the GES.
Posted By: mikeD Re: grounding direct tv - 02/02/10 08:32 PM
The dish is at one end of the house and the panel is at the other end not that far about 40 feet. what size wire should that be #6. The biggest question is why wasent that done when it was put in.direct tv free install nothing free about direct tv every time you turn around your getting a notice about a rate increase. guess that what happenes when you live in the sticks and they are the only way you can watch tv..
Posted By: EV607797 Re: grounding direct tv - 02/02/10 10:51 PM
#6 is fine to bond them together. As to why they didn't do this: It all comes down to the installer. They usually work as sub contractors and are paid piecemeal, so the fastest way in and out is usually all that you get.
Posted By: HotLine1 Re: grounding direct tv - 02/03/10 12:11 AM
Hence, 250.95 ('08 NEC) requires the intersysten bonding location.

BTW, the dish guys here are not much more professional in the workmanship dept.

Heck, last week I came upon a pipe clamp on PVC at the meter! I thought they outgrew that stupidity.

Posted By: mikeD Re: grounding direct tv - 02/03/10 01:49 PM
You can't fix stupid