Posted By: JG Scheldule 80 - 06/08/05 10:29 PM
Would it be permissible to use sch 80 in a hospital, with two grounds as long as you did not supply patient areas or emergency power through it?(You would still use a mettallic raceway for these areas)
Posted By: Tech-Home Re: Scheldule 80 - 06/09/05 01:56 AM
I don't think that you can use PVC in a hospital under any circumstance. I have never seen PVC in the hospital that I worked in.
Posted By: Yoopersup Re: Scheldule 80 - 06/09/05 12:07 PM
517.13 a wiring methods,
517.30c(3) Exceptions 3& 4 Essential Electrical Systems
Posted By: Roger Re: Scheldule 80 - 06/09/05 02:00 PM
JG, there is no need to put two EGC's in PVC in a hospital.

In the applications where PVC can be used in a hospital, there would be no reqirement for this to be done.

See Yoopersups' code references, as well as 517.12


Roger



[This message has been edited by Roger (edited 06-09-2005).]