Posted By: George Little Receptacle - 05/19/05 04:20 AM
Would I be required to install a 15 or 20 ampere 125v. receptacle in a detached building (not a garage) at a residence? Or, could this be an option? All the contractor installed was a luminaire.
Posted By: gfretwell Re: Receptacle - 05/19/05 04:44 AM
The light in a detached utility building is a luxury, not a requirement, nor is a receptacle.
As a design issue I can't imagine bringing 120v out to a utility building for a light and not putting in a receptacle but I am not sure how you can require it.
Posted By: shortcircuit Re: Receptacle - 05/19/05 10:36 AM
George Little...the code does specifically state "detached garages" under 210.52(G)

I'm with gfretwell on this one, no the receptacle outlet is not required.

Although, I would put one in if I wired that building [Linked Image]

shortcircuit
Posted By: iwire Re: Receptacle - 05/19/05 09:56 PM
Quote
Although, I would put one in if I wired that building

[Linked Image]

I agree.

You know I can not even believe someone would leave out a receptacle outlet in a case like this. [Linked Image]


Still....Glad it's not a code requirement. [Linked Image]
Posted By: Ryan_J Re: Receptacle - 05/20/05 01:15 PM
210.52(G) requires a receptacle outlet, if the detached garage has power.

Edit: Sorry, looks like somebody already said that...thats what I get for posting before having some coffee [Linked Image]

[This message has been edited by Ryan_J (edited 05-20-2005).]
Posted By: George Little Re: Receptacle - 05/20/05 01:38 PM
Get another cup of coffee Ryan [Linked Image] This is not about a garage [Linked Image]
Posted By: Ryan_J Re: Receptacle - 05/20/05 04:53 PM
[Linked Image]