Posted By: Electric Ian 20 amp GFCI receptacles - 05/17/05 11:35 AM
I often run across a 20 Amp GFCI receptacle feeding 15 amp receptacles on the 20 amp kitchen appliance and bathroom receptacle circuits. Isn't this a code violation? Not the fact that 15 amp receptacles are on a 20 amp circuit but the fact that a 20amp rceptacle is on the circuit with other receptacles.
Posted By: earlydean Re: 20 amp GFCI receptacles - 05/17/05 03:11 PM
nope
Posted By: Ryan_J Re: 20 amp GFCI receptacles - 05/17/05 05:12 PM
See table 210.24 for a nice summary of what you are discussing.
Posted By: Larry Fine Re: 20 amp GFCI receptacles - 05/19/05 02:58 AM
The only difference between 15- and 20-amp receptacles (of the same grade) is the slot shape. Ever notice that 15-amp GFCI receptacles are rated for 20 amps on the feed-through terminals?