Posted By: watersparkfalls stranded 14 awg - 05/06/05 05:33 AM
true or false stranded wire cannot be connected on a scew terminal(i.e. switch)
without the use of a terminal knife/ring connector? please reference nec article.

h2O
Posted By: iwire Re: stranded 14 awg - 05/06/05 09:29 AM
All UL listed devices for use with 14, 12 and 10 AWG are suitable for solid or stranded conductors.

That info. can be found in the UL White book.
Posted By: Redsy Re: stranded 14 awg - 05/06/05 11:53 PM
Yes, UL White Book page 100 under "Termnial" subheading of the "Receptacles for Attachment Plugs and Plugs (RTRT)" heading