Posted By: Steve Miller 680 GFCI Protected wiring - 04/27/05 10:26 AM
This quote is from 680-5 in the 99 code:
"(c) Wiring. Conductors on the load side of a ground-fault circuit interrupter or of a transformer, used to comply with the provisions of section 680-20(a)(1), shall not occupy raceway, boxes, or enclosures containing other conductors unless the other conductors are protected by ground-fault circuit interrupters or are grounding conductors."
Anybody know where this is in the 02 code? or is it removed?
Posted By: gfretwell Re: 680 GFCI Protected wiring - 04/27/05 03:52 PM
680.23(F)(3) if this is the light.
Posted By: Steve Miller Re: 680 GFCI Protected wiring - 04/27/05 06:58 PM
That's it ...thanks ... I must have looked for an hour and couldn't find it.