Posted By: electcontrctr Service Load Calculated at 125%? - 04/07/05 06:53 PM
Hello,
Is the Service Load Calculated at 125% for a single family dwelling?

Can I use 65% of the nameplate rating for a heat pump system?

Thank you,

Brad
Posted By: Tom Re: Service Load Calculated at 125%? - 04/09/05 08:58 PM
1. No

2. No, but you might be able to use 65% of the supplemental electric heat.

Check out example D2(c) in Annex D for an example (2005 NEC)

Tom