Posted By: sawdust454 Motor fuel dispensing area? - 03/21/05 01:36 PM
I have a costumer with a newly installed diesel standby generator that has a 500 gallon tank within 3'. They want to dispense fuel from this tank to a fleet of trucks, I believe this installation must follow article 514 to be compliant. It has a pump mounted on top of the tank and is an outdoor installation. Any thoughts!
Thanks
Posted By: George Little Re: Motor fuel dispensing area? - 03/21/05 02:53 PM
This installation is not subject to Article 500. Use any of the wiring methods in Article 300 that are suitable for the environment.
Posted By: safetygem Re: Motor fuel dispensing area? - 03/21/05 03:20 PM
sawdust454... George is correct. The presence of diesel fuel does not create a "classified" area. This of course assumes that there isn't a gasoline tank nearby the diesel tank. [Linked Image]

If you want more information, you should research NFPA 30A-2003, Code for Motor Fuel Dispensing Facilities and Repair Garages. This is the standard that classifies motor vehicle fuel dispensing areas.

You can review a "read-only" copy of 30A on-line at: http://www.nfpa.org/itemDetail.asp?...lopment%20process/Free%20online%20access

Hope this helps.
Posted By: sawdust454 Re: Motor fuel dispensing area? - 03/21/05 06:28 PM
Thanks guys, I feel a little better about this installation.