Posted By: ronaldsax line and load, and derate - 01/31/05 05:11 PM
Hi
I just have 2 quick questions
can I have line and load in the same raceway?
and what is derating?

thank you
Posted By: Yoopersup Re: line and load, and derate - 01/31/05 08:53 PM
I;d say yes and derateing by 310.15(B)2
Posted By: earlydean Re: line and load, and derate - 01/31/05 08:56 PM
Line and load is OK in the same raceway, but service and feeder, or service and branch circuit conductors cannot be in the same raceway.
De-rating is contained in the bottom section of Table 310.16 for ambient temperature, and in Table 310.15(B)(2)(a) for more than 3 current carrying conductors in a raceway or cable, or bundling of cables