Posted By: eswets Closet lights - 01/06/05 05:16 AM
I need some help with this one. If you have a closet that is 24" deep can you install a light in there? I've read the codes and it gets a little confusing. If you use a dome covered pullchain, you have to be 12" from the egde of the self (the selfs are usually 12") and 6" from the other wall. You will need a 36" Closet to do this. A can light can be 6" from edge so with that you need a 30" closet. Am I just messing this all up or am I right, b/c all of the prints I get have 24" closets with lights in them.
Posted By: Physis Re: Closet lights - 01/06/05 05:32 AM
If your closet is only 24" deep you will need to use recessed.

And the edge of the recessed fixture toward the rear has to be 18" from the rear wall.

And the shelf if any must be 6" from the edge of the fixture.

That doesn't address the 6' or hight of hanger rod off the floor.
Posted By: Norstarr Re: Closet lights - 01/06/05 05:46 AM
Install a covered fluorescant fixture over the door and your covered. Very nice light and if you want a pull chain it will be right by the door. If you have Menards by you they have a fluorescant just for that with a pull chain.
Ron
Posted By: Physis Re: Closet lights - 01/06/05 07:49 AM
410.8(D)(2)seems to allow it. I think you're right Ron.

My Charles Miller disagrees but who's he?
Posted By: George Little Re: Closet lights - 01/06/05 01:52 PM
The fluorescent doesn't have to be covered if it's 6" from the storage space but I would recommend that it is, 410.8(D)(2).
Posted By: GTE Re: Closet lights - 01/06/05 10:48 PM
George,
Flourescents have to be 6" from from the storage area whether it is covered or not.
Posted By: George Little Re: Closet lights - 01/06/05 11:03 PM
GTE- I agree and my wording was poor so I appreciate the clarification. Could also be noted that the storage space below the shelf is often times larger than above the shelf and the clearances apply here too.
Posted By: mike d Re: Closet lights - 01/06/05 11:48 PM
how wide is the closet? keep in mind 410.8 says storage space is the sides & back wall,
a 12" shelf is figured on sides & back wall
even if no shelfs are installed, you must also take the side walls into consideration
also.
Posted By: eswets Re: Closet lights - 01/07/05 12:47 AM
So if there is no self in the closet, can the light be in the middle of a 24" closet? Or do you have to assume that one day someone can put in a self.
Posted By: Physis Re: Closet lights - 01/08/05 01:24 AM
I just decided that this section is so terribly writen that I could solve the Rubix cube before sorting this mess out.

Good luck.
Posted By: Norstarr Re: Closet lights - 01/10/05 07:16 AM
Like I said, a fluorescant fixture above the door and you don't have to worry about the clearances. Have used typical undercounter type that are covered. Menards has them with pull chains and are called closet fluorescents. Can't seem to put to memory the rules for closets so I have to lay it out everytime I need to light one.
Ron