Hi,
I know that a drip loop has a 3 foot clearance from any window or door but what about a meterbase that is fed from a service lateral?
I do not think the code addresses that do they?
I know there is a height requirement usually 5-6-6" around here.
Thanks for any replies.
-regards
Greg
I would have to say no. Look at 230-9(A). Unless your lateral is open conductors or a multiconductor cable without a overall outer jacket, It can be as close to the window as you like. A meter socket is accessible from the ground, so why would it matter if the conductors where 3' from a window, when I could go outside and touch them?
Hi,
Thanks for the reply..I do not know what the feeder will be because the POCO installs the feeder from their xfmr to the meterbase using the 3" conduit I installed.
What is the requirement with a multiconductor cable underground?
-regards
Greg
http://www.portlandgeneral.com/business/builders_and_dev/PDF/chapter5.pdf http://www.portlandgeneral.com/business/builders_and_dev/PDF/chapter3.pdf Meter clearances hear must apply to Electric service requirements from local power company.
Its a good idea to get a current ESR from your local power co.Has all the information,clearences and requirements