Posted By: mustangelectric SE Conductor Ampacity - 11/29/04 06:02 PM
Hi,
What article allows 2/0 copper for a 200A service? This is a residential application. It is 310.15(B)(6) isnt it?

IS there a table for commercial service entrance ampacity?

Thanks for any replies.

-regards

Greg


[This message has been edited by mustangelectric (edited 11-29-2004).]
Posted By: iwire Re: SE Conductor Ampacity - 11/29/04 07:41 PM
No special table for other than dwelling units.

For a commercial service you will use 310.16 and the 75 C column.
Posted By: John M Caloggero Re: SE Conductor Ampacity - 11/29/04 11:53 PM
Hi Greg: you are correct,Table 310.16(B)(6) is allowed to size the service conductors for a dwelling.