Posted By: aldav53 Plastic boxes/Commercial use - 11/03/04 06:01 AM
Are plastic boxes ok to use in commercial buildings? Some do have a knockout for pipe or mc cable to run into.
Posted By: electricman2 Re: Plastic boxes/Commercial use - 11/03/04 06:05 PM
Non-metallic boxes cannot be used with metallic wiring methods unless meeting one of the two exceptions. 314.3.
Posted By: aldav53 Re: Plastic boxes/Commercial use - 11/04/04 04:12 AM
Why then is there a 1/2" knockout? for PVC? What would be wrong with plastic boxes, there used in homes?
Posted By: caselec Re: Plastic boxes/Commercial use - 11/04/04 06:09 AM
The non-metalic boxes with standard K.O’s are for ENT (smurf tube) or can be used with RNMC. There is nothing wrong with non-metallic boxes when used with non-metallic wiring methods. You can’t use metal raceways or cable armors with non-metallic boxes since the raceway or armor would not be properly bonded.

Curt
Posted By: aldav53 Re: Plastic boxes/Commercial use - 11/04/04 04:17 PM
caselec,
Yes true, unless you run metal cable from a bonded metel panel to the plastic box, then its bonded at one end.
Posted By: zapped208 Re: Plastic boxes/Commercial use - 11/04/04 08:52 PM
electricman2 has the correct response.
I wonder if a twin M/C connector would satisfy the exception to 314.3?