Posted By: aldav53 Liquid-tite - bends - 04/21/04 03:12 PM
Is there a limit on the amount of bends when running liquid-tite or other flexible conduit?
Posted By: NJwirenut Re: Liquid-tite - bends - 04/21/04 03:59 PM
No more than 360 degrees total between access points, like any other conduit system.
Posted By: aldav53 Re: Liquid-tite - bends - 04/21/04 10:43 PM
You would think it might be different because you can run the wire inside before you install the flexible conduit. But if you ever have to pull it out later, could be tuff.
Posted By: iwire Re: Liquid-tite - bends - 04/21/04 10:47 PM
Yeah you can do that, and I am sure we all have done it, but code wise we are not suposed to.

Quote
300.18 Raceway Installations.
(A) Complete Runs.
Raceways, other than busways or exposed raceways having hinged or removable covers, shall be installed complete between outlet, junction, or splicing points prior to the installation of conductors. Where required to facilitate the installation of utilization equipment, the raceway shall be permitted to be initially installed without a terminating connection at the equipment. Prewired raceway assemblies shall be permitted only where specifically permitted in this Code for the applicable wiring method.
Posted By: dannynova Re: Liquid-tite - bends - 04/28/04 09:26 PM
how far are you running the liquid flex if your worried about more than 360 degrees of bends. usually a six foot piece has much less than 360 in bends
Posted By: iwire Re: Liquid-tite - bends - 04/28/04 09:42 PM
You can run flex as far as you like. [Linked Image]