Doing work in a warehouse (1800ft). Is there a code for required outlets? I know there is for dwellings but how about warehouses? Do you space them 12' apart?
You will find what you're looking for in article 210. Article 406 may be applicable also.
Roger
Zapper,
A fellow Long Islander I see!
Generally speaking, there's no minimum requirements for general purpose receptacles.
Bill
Thanks Bill- I was sure there wasn't. Article 210 does not have a requirement for outlets in warehouses. But its
great to get another voice on it.
Zapper
I took a teaching class with two electricians from Ronkonkamo, Long Island in January.
Pierre
Pierre,
That's spelled Ronkonkoma
I'm in the next town over.
Bill
See also 210.62 and 210.63