Posted By: rknikko Panel in hallway... - 02/23/04 03:01 AM
Can I move the existing panels from the basement to the ground level public hallway in a 2 family house. I'm doing this because I am moving the existing meters from the basement to the outside of the house? Normally, the panel will be in the tenant's unit, but in this case I am not sure whether it can be installed in the hallway or not. Please help. Thank you.
Posted By: russ m Re: Panel in hallway... - 02/23/04 01:40 PM
I can't see why not as long as they have access to the breakers.
Also the installation would have to be compliant with 230.70 and 110.26
Posted By: Electricmanscott Re: Panel in hallway... - 02/23/04 10:56 PM
I have to ask, why not leave the panels in the basement?
Posted By: rknikko Re: Panel in hallway... - 02/23/04 11:28 PM
Owner's request.